Inputs & outputs & relays ohmic
Now was moving onto the actual control of the plasma its self. I'm going to use a hyperthermia 30XP so I don't have an interface on the plasma to connect to. I'm guessing I'm going to need a relay for the torch start. Does that need to be a DPDT NO. That way the 7i76 knows when it's not triggered by feeding back through the closed leg? I will be using a thcad10 which I know will need some resistors to work with the 30XP. I do have a floating Z with a NC switch. It's set up so when the torch touches off the slide lifts off the switch closing it. It's a very accurate switch designed for tool setters for cnc machines.
The next question is incorporating ohmic and what relays I need for that. I'm guessing I can use the 30XP as it's consumables are shielded except the the fine cut.
I'm guessing there is some clever relay circuitry to incorporate this all together and prevent blasting the 7i76ED with 300v when it fires. And speaking of firing how is the arc ok signal generated for LinuxCNC to see. I would think it would involve an amp reading which is sent back to the analog inputs. But I could be way off.
Thanks guys for any tips or help you can provide. I'm so close to cutting I can taste it lol.
JTknives
Please Log in to join the conversation.
1. Stepper motor disable on estop (optional but due to having an estop on a wireless pendant)
2. Torch on relay but PCW has suggested using the spindle output on the 7i76 so you might be able to drop it
3. Ohmic enable relay (triggered by an output)
4. Ohmic sensing relay (input)
5. IN4007 1000 volt diode
6. Dedicated 24 volt isolated power supply Meanwell 0.5 amp approx
I think I have it right. For the arc, the torch is negative and the work piece is positive.
So the isolated ohmic power supply (-24v) is earthed to the table
My wire on the torch is 24v positive
The Ohmic sensing relay is triggered when the shield touches the workpiece and sends 24v field power to an input but:
The Enable relay ensures the power to the ohmic sensing relay is only enabled when probing and turned off at other times.
The diode will prevent a reverse current flow if something goes wrong with the arc voltage.
Initially, I had the -24v going through a diode to earth as well but I had some spurious voltage potentials floating around between the torch and the table so took the diode out of the equation.
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
- Posts: 22010
- Thank you received: 3
Oh no, not hyperthermia please !!!JTknives wrote: I'm going to use a hyperthermia 30XP ......
hy·per·ther·mi·a
/ˌhīpərˈTHərmēə/
nounMedicine
noun: hyperthermia
the condition of having a body temperature greatly above normal.
Please Log in to join the conversation.
Please Log in to join the conversation.
rodw wrote: I think I've ended up with 4 relays on my machine
1. Stepper motor disable on estop (optional but due to having an estop on a wireless pendant)
2. Torch on relay but PCW has suggested using the spindle output on the 7i76 so you might be able to drop it
3. Ohmic enable relay (triggered by an output)
4. Ohmic sensing relay (input)
5. IN4007 1000 volt diode
6. Dedicated 24 volt isolated power supply Meanwell 0.5 amp approx
I think I have it right. For the arc, the torch is negative and the work piece is positive.
So the isolated ohmic power supply (-24v) is earthed to the table
My wire on the torch is 24v positive
The Ohmic sensing relay is triggered when the shield touches the workpiece and sends 24v field power to an input but:
The Enable relay ensures the power to the ohmic sensing relay is only enabled when probing and turned off at other times.
The diode will prevent a reverse current flow if something goes wrong with the arc voltage.
Initially, I had the -24v going through a diode to earth as well but I had some spurious voltage potentials floating around between the torch and the table so took the diode out of the equation.
Are you saying that pins 5&6 on TB4 can be used to close the torch start switch?
Please Log in to join the conversation.
- islander261
- Offline
- Platinum Member
-
- Posts: 757
- Thank you received: 0
2. The ohmic enable relay is to physically disconnect the sensing circuit from the work piece and torch shield when not probing. This needs to a single Double Pole (DP) or two Single Pole (SP) (what I have) relays.
3. You must be sure the power supply is truly isolated. This causes the most problem for people. Check that the output minus is not internally connected to the safety ground, third wire or DIN rail clamp or to the neutral wire.
4. Please find attached the circuit I have used for several years with no problems.
John
Attachment not found
Please Log in to join the conversation.
JTknives wrote:
Are you saying that pins 5&6 on TB4 can be used to close the torch start switch?
Yes, I believe so.
Please Log in to join the conversation.
islander261 wrote: 1
2. The ohmic enable relay is to physically disconnect the sensing circuit from the work piece and torch shield when not probing. This needs to a single Double Pole (DP) or two Single Pole (SP) (what I have) relays.
Hmm, thanks, I'll change some wiring on the workpiece side. Something was worrying me.
I know you've shared that circuit several times but when I needed it, I couldn't find it.
Please Log in to join the conversation.
now onto the question(s)
Can I just run my probe sensing through a crydom M505012F. I have 2 just laying around and been looking for a use for them. here is their layout. also my 7i76 is the ED version so its outputs are syncing not sourcing.
Attachment not found
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
- Posts: 22010
- Thank you received: 3
Unfortunately no, those are SCR used for switching AC, not DC.JTknives wrote: Can I just run my probe sensing through a crydom M505012F.
The problem with them is that once opened they will remain opened until there is not more current flowing through them and that is something that in AC happens 50 or 60 times per second while in DC it does not until the power is cut off.
Also that is a non isolated type so in the future if you use them, keep that in mind.