Shielded cable - Attaching the drain
5 years 8 months ago #198163
by txtrone
Shielded cable - Attaching the drain was created by txtrone
I know it's important to attach the shield/drain cable to the cabinet ground only, not at the motor. What about other locations where shielded cable has been used? My power supplies are in a separate cabinet than my mesa board and drivers, the cable I used has a shield... should I connect it at all?
What about sensor cables, if they have a shield, should they be connected on either end?
Thanks
What about sensor cables, if they have a shield, should they be connected on either end?
Thanks
Please Log in to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
Less
More
- Posts: 4739
- Thank you received: 2
5 years 8 months ago #198170
by Todd Zuercher
Replied by Todd Zuercher on topic Shielded cable - Attaching the drain
Cable shields should always be connected only at one end.
Please Log in to join the conversation.
5 years 8 months ago #198174
by txtrone
In the case where shielded cable is run between two cabinets, carrying power from the PSUs to the Mesa and driver boards... does it matter which side the shield is connected?
Thanks
Replied by txtrone on topic Shielded cable - Attaching the drain
Todd Zuercher wrote: Cable shields should always be connected only at one end.
In the case where shielded cable is run between two cabinets, carrying power from the PSUs to the Mesa and driver boards... does it matter which side the shield is connected?
Thanks
Please Log in to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
Less
More
- Posts: 4739
- Thank you received: 2
5 years 8 months ago #198176
by Todd Zuercher
Replied by Todd Zuercher on topic Shielded cable - Attaching the drain
Probably not, but it is generally best to try to keep them as common as possible (star grounding).
Please Log in to join the conversation.
5 years 8 months ago #198186
by txtrone
Thanks! I will ground them all in the 'control cabinet'.
Replied by txtrone on topic Shielded cable - Attaching the drain
Todd Zuercher wrote: Probably not, but it is generally best to try to keep them as common as possible (star grounding).
Thanks! I will ground them all in the 'control cabinet'.
Please Log in to join the conversation.
- Mike_Eitel
- Offline
- Platinum Member
-
Less
More
- Posts: 1018
- Thank you received: 0
5 years 8 months ago #198380
by Mike_Eitel
Replied by Mike_Eitel on topic Shielded cable - Attaching the drain
If you need to have better emf protection connect them via parallel RC to ground on second side. Take a good capacitor. Even you could meassure the voltage over the resistor. Such connection is by the way my way of connecting all my psu's to the central earthing point of my cnc. My R's are in the few hundred ohms. An i do dislike to see dc-volts over them ;-().
Mike
Mike
Please Log in to join the conversation.
5 years 8 months ago #198455
by Michael
Replied by Michael on topic Shielded cable - Attaching the drain
Often you will find specific instructions for control and signal wiring in regards to the shield and how it should be grounded. The 7i77 boards specify to have the analog output shields grounded to the analog negative.
From my limited experience control signaling cables will be shield grounded to the device sending the signals and only to the one end. Typically one of the wires establishes common between the two devices.
From my limited experience control signaling cables will be shield grounded to the device sending the signals and only to the one end. Typically one of the wires establishes common between the two devices.
Please Log in to join the conversation.
Time to create page: 0.096 seconds