4 years 8 months ago #234213 by salem747
Hi guys,

Having a hard time figuring out my float switch. I am using a microswitch and I assumed (and from what I understand in the Mesa manual) it would go one conductor as an input and the other to the input common on the 7i96. I have looked at the wiring diagrams available and none of them are quite like what I am doing.

TIA.

Please Log in to join the conversation.

More
4 years 8 months ago #234216 by phillc54
Replied by phillc54 on topic Float switch on 7i96
I have a 24V field power supply:
0V connected to input common.
24V connected to the float microswitch.
The other side of the float microswitch connected to input8.
 

Please Log in to join the conversation.

More
4 years 8 months ago #234217 by PCW
Replied by PCW on topic Float switch on 7i96
7I96 inputs are wired like this:

For sourcing inputs

Input common (TB3 pin 12) <-- +5 to +24V
Inputs 0 through 10 (TB3 pins 1 through11) connect to
ground (+5V +24V common) to activate

For sinking inputs

Input common (TB3 pin 12) <-- ground
Inputs 0 through 10 (TB3 pins 1 through11) connect to
+5V ... +24V to activate

Please Log in to join the conversation.

More
4 years 8 months ago #234268 by salem747
Replied by salem747 on topic Float switch on 7i96
And what is the difference between sourcing and sinking? Just in the way you set them up?

If I read correctly, the easiest setup is provide 24v to the microswitch and then the opposite side of the switch to an input on Mesa, when switch closes I get a 24v signal to the input, telling Mesa that the switch is activated. So sinking?

I still don't understand how the common works. I have a bunch of npn sensors, I provide them with field voltage and the signal wire to an input on the Mesa, linuxcnc sees those just fine.

Please Log in to join the conversation.

More
4 years 8 months ago #234276 by PCW
Replied by PCW on topic Float switch on 7i96
For sourcing inputs (that work with NPN sensors)
The input common goes to +5..+24V

For sinking inputs the input common goes to ground

So if you have NPN sensors, you should connect the
input common to +24V, and any switches would
connect the 7I96 inputs to ground