How do you pass shielded servo motor cables through the cabinet wall/panel?

More
05 Aug 2022 12:27 #249113 by mgm
The side on the Antieb is open with me

Please Log in or Create an account to join the conversation.

More
05 Aug 2022 12:44 #249115 by arvidb

So if you use a ground clamp as suggested by above links above, how do you connect the shield to the drive connector terminal block?

You don't. Look at the Siemens video I linked above.

Note that you must still connect the ground conductor between the motor and the drive terminal, for safety.

Please Log in or Create an account to join the conversation.

More
05 Aug 2022 13:09 #249117 by mgm
I wouldn't know where to put the screen on my milling spindle. The junction box is in plastic.

A grounding cable is of course present!

Please Log in or Create an account to join the conversation.

More
05 Aug 2022 19:02 #249150 by rodw

So if you use a ground clamp as suggested by above links above, how do you connect the shield to the drive connector terminal block?
You don't. Look at the Siemens video I linked above.

Note that you must still connect the ground conductor between the motor and the drive terminal, for safety.

The video shows use of a cable for servos with an additional ground conductor. In the case of a 4 wire stepper system, some quality stepper drives require the shield to be terminated at the drive as this diagram from the manual of a Lam Technologies DS1076A shows.
 
Ref: www.lamtechnologies.com/Product.aspx?lng=EN&idp=DS1076
Elsewhere, they suggest the cable pass through the cabinet intact (eg. via a cable grommet) 

When I've used these drivers, I've also terminated the shield to a copper grounding post on the enclosusre as shown here.
 

Note we've deliberately chosen steppers over servos in this application (plasma table) to leverage the massive acceleration steppers provide. (5 m/sec/sec or higher)
 
Attachments:

Please Log in or Create an account to join the conversation.

More
05 Aug 2022 19:27 #249153 by rodw
So from my post above, I am still confused somewhat but it seems one thing that both Siemens and Lam have in common is not to use any connectors where the cables enter the cabinet. Elsewhere in the Lam manual it shows:
 
I guess use of a grounding clamps could be used instead of my pigtails to frame ground.

So best practice for both steppers and servos is not to do any soldering. Yippee! :)
Attachments:

Please Log in or Create an account to join the conversation.

More
06 Aug 2022 03:41 #249176 by arvidb

I guess use of a grounding clamps could be used instead of my pigtails to frame ground.

Since the drives look to be insulated from the cabinet's grounded mount plate, connecting the shield with a clamp to the plate won't do you any good as I understand it. You are probably best off just following the instructions in the manual, paying close attention to the "it must be as much short at possible" part. :)

I don't see anything about EMC compliance in the publicly available documentation for those drives. Maybe it's in the User Manual that's behind a registration wall? *doh* Maybe these drives aren't designed to meet any specific EMC standard and controlling EMI is just an afterthought? Or maybe they are controlling the rise times of the motor driver FETs to not produce high frequency EMI in the first place (at the expense of more heat) and have calculated that the pigtail connection of the shield is enough. Who knows?

Please Log in or Create an account to join the conversation.

More
06 Aug 2022 04:24 #249177 by arvidb

I wouldn't know where to put the screen on my milling spindle. The junction box is in plastic.

Yeah I have similarly been scratching my head about how to connect the shield to these old servos:


But after reading about how the shield is the return path of common mode noise between motor frame and drive, I think a good solution is to attach the incoming cable shield with a P-clip to the aluminium plate that the motor will be mounted to. That should provide a low impedance path from the motor frame to the shield. I hope. At least that's the best idea I've been able to come up with!
Attachments:

Please Log in or Create an account to join the conversation.

More
06 Aug 2022 05:30 #249181 by rodw
@avidb, Normally you would leave the shield unattached at the motor and attach it to frame ground at the enclosure. I think you would use one of your grounding clamps as normal.
If for a plasma machine, you should attach a seperate ground wire from every motor that is run  seperately back to the star ground point. Some industrial quality stepper motors actually have a screw terminal for this purpose. Alternatively use one of the motor mounting bolts. You also need to ensure that these ground wires bridge any motion rails to avoid EMI passing through the rail and its carriage. Hypertherm have a good tech note on grounding which I follow. www.hypertherm.com/Download?fileId=HYP103900&zip=False
Its probably best practice for any motor that does not have a dedicated ground wire.

So I suspect This would explain why Lam do it the way they do. The EMI is drained away by the grounding system.

Please Log in or Create an account to join the conversation.

More
06 Aug 2022 07:10 #249183 by arvidb

@avidb, Normally you would leave the shield unattached at the motor and attach it to frame ground at the enclosure.

I'm not sure why you would say that since it's exactly the opposite of what's recommended by the sources I gave earlier. E.g. from the Danfoss document:

It is important to realize that the effect of a shielded cable is reduced when only one end is terminated. It is very important to terminate correctly both ends of the motor cable, otherwise interference problems may occur.


Most importantly, the two written sources explain their reasoning in a way that makes sense. Your call...

So I suspect This would explain why Lam do it the way they do. The EMI is drained away by the grounding system.

Which is exactly what you want to avoid since it creates a big current loop for the noise to radiate from. See the Electrical Engineering Portal images. You also want to keep the motor noise away from ground circuitry used by other equipment to which it can otherwise be conducted. You want the noise return path to be through the shield, not through motion rails or paths shared with feedback circuitry.

Please Log in or Create an account to join the conversation.

More
06 Aug 2022 07:35 - 06 Aug 2022 07:44 #249184 by Aciera
Using pigtails to connect cable shielding is generally bad practice. Although I readily admit to have done it myself in the past. Of course EMI protection is more important in some installations than in others but motor drives being notorious for producing electromagnetic interference should be handled with extra diligence.

There is a ton of information on the web covering this. Here are just a few examples:
www.edn.com/never-use-pigtails-on-cable-shields/
www.rfemcdevelopment.eu/lv/emc-basics/emc-blog/147-emc-pigtail


In a cabinet one can use a ground busbar like this:
www.phoenixcontact.com/en-au/technologie...-in-control-cabinets

Personally I use P-Clamps and bolt those to busbars or the grounded backplate in the cabinet as those shield clamps can get a bit pricey. The only reason I see why companies like LAM suggest the use of (short) pigtails is to make wiring of their product look "easier".
The installation manual of a name brand VFD is usually a good source for proper grounding techniques.
But att the end of the day it's still a lot better to use shielded cabling with short pigtails than using unshielded cabling.

Edit
Just to be clear, I don't mean to be in anyway authorative about the matter or put anybodies work down. But since this has come up I thought I'd share what I had to learn (sometimes the hard way) in the past.
Last edit: 06 Aug 2022 07:44 by Aciera.
The following user(s) said Thank You: arvidb, Clive S

Please Log in or Create an account to join the conversation.