How to wire MPG on 7i77?
12 years 6 months ago - 12 years 6 months ago #46036 by PCW
Replied by PCW on topic How to wire MPG on 7i77?
Using field I/O pins with the software encoder can work but has some problems. If you use a standard 12 or 24V field I/O voltage for noise immunity and relay/solenoid driving capability, the inputs will not be compatible with 5V MPG signals. Also unless you use a low resolution encoder, it will be easy to mis-count. For example, with your 256 PPR encoder (1024 counts per turn) turning the shaft faster than 1 turn per second will result in lost counts.
Since you have fast 5V input hardware counters available, it better to use them
for example, to use one of the servo interface encoders (channel 4 here) for the MPG
you just replace:
net mpg-out encoder.0.rawcounts => ilowpass.0.in
with
net mpg-out hm2_5i25.0.encoder.04.rawcounts => ilowpass.0.in
and delete these software encoder HAL lines as they are not needed:
loadrt encoder num_chan=1
addf encoder.update-counters servo-thread
addf encoder.capture-position servo-thread
net mpg-a hm2_5i25.0.7i77.0.0.input-14 => encoder.0.phase-A
net mpg-b hm2_5i25.0.7i77.0.0.input-15 => encoder.0.phase-B
similarly, to use the 7I77s field I/O MPG inputs you would replace
with
net mpg-out hm2_5i25.0.7i77.0.0.enc0 => ilowpass.0.in
(and also deleting all the software encoder related lines)
But to make the MPG encoder available you need set the field I/O sections process data mode to 3 by adding a "sserial_port_0=300xxx" stanza to the hm2_pci config string (setting sserial modes is documented in the hostmot2 manual)
Note that the encoder name for sserial devices will change in LinuxCNC version 2.6
Last edit: 12 years 6 months ago by PCW.
The following user(s) said Thank You: greeder88
12 years 6 months ago #46046 by greeder88
Replied by greeder88 on topic How to wire MPG on 7i77?
That is fantastic. I couldn't be happier.
Here it is in changed form so the next lost wannabe MPG Jogger will just have to copy it and go.
#Jog Pendant
loadrt mux4 count=1
loadrt ilowpass
setp ilowpass.0.scale 100
setp ilowpass.0.gain 0.01
addf mux4.0 servo-thread
addf ilowpass.0 servo-thread
net x-jog-select axis.0.jog-enable <= hm2_5i25.0.7i77.0.0.input-00
net y-jog-select axis.1.jog-enable <= hm2_5i25.0.7i77.0.0.input-01
net z-jog-select axis.2.jog-enable <= hm2_5i25.0.7i77.0.0.input-02
#net a-jog-select axis.3.jog-enable <= hm2_5i25.0.7i77.0.0.input-03
net x10 hm2_5i25.0.7i77.0.0.input-08 => mux4.0.sel0
net x100 hm2_5i25.0.7i77.0.0.input-13 => mux4.0.sel1
setp mux4.0.in0 .0000025
setp mux4.0.in1 .000025
setp mux4.0.in2 .00025
setp mux4.0.in3 .0
net jogscale mux4.0.out => axis.0.jog-scale
net jogscale => axis.1.jog-scale
net jogscale => axis.2.jog-scale
#net jogscale =>axis.3.jog-scale
net jogcounts ilowpass.0.out => axis.0.jog-counts
net jogcounts => axis.1.jog-counts
net jogcounts => axis.2.jog-counts
#net jogcounts => axis.3.jog-counts
12 years 6 months ago #46055 by andypugh
Replied by andypugh on topic How to wire MPG on 7i77?
greeder88 wrote: What does the "xxx" on the end mean? Why is there 3 X's? And or what document has the info?
www.linuxcnc.org/docs/html/man/man9/hostmot2.9.html
Under "config modparam"
I agree that that manpage probably needs reworking.
12 years 6 months ago #46074 by greeder88
This is definitely complicated stuff. If you think about it just wiring the connections can tie your head in a knot. But it sure is fun when you get success!.
I'm planing on doing a web page to make this way simpler for the electronics simpletons such as myself. That should be fun.
Not that much left to do...
The end is near.
12 years 6 months ago #46106 by greeder88
I'm using the Field IO Mpg configuration and pretty sure everything is configured right except I need to change from the default 100cpr scale.
Following the previous suggestion I need to change jumpers for single ended outputs.
Using encoder 05 pins 17,20,23.
There are three jumpers. Which jumper is the one I have to change?
12 years 6 months ago #46108 by PCW
W9 and W7 should be moved to the left hand position for single ended A,B encoder signals on encoder 5
The index (TB4 pin 23 and jumper W3) need not be connected/changed since index is not used for jogging.
Note that this is not a field I/O MPG connection but rather using a
normal servo feedback encoder input for a MPG.
(the field I/O MPG encoder inputs are on TB7 pins 16,17,18, and 19)
Moderators: PCW, jmelson