Choice of encoder for 7i76 + Pathpilot
8 years 4 months ago #111849 by Robi63
I have tested in PP with Halmeter
in pins hm2-5i25.0.gipo.015.in / 016.in are OK 014.in no signal
in signal I tested spindle-phase-A / B are OK Z no signal even spindle-index-enable no signal.
8 years 4 months ago - 8 years 4 months ago #111868 by PCW
I would not expect to see the index signal, that's why you must test for it in the way I indicated
This is because the index signal is a very short pulse on a high resolution encoder and its easy to miss
because of both the 1 KHz servo thread sampling and the fact that halmeter or "show" are only sample
hal data at about a 10 Hz rate
Last edit: 8 years 4 months ago by PCW.
8 years 4 months ago #111934 by Robi63
Hi PCW,
As always, you're right.
I have done your test and one point passes from true to false.
In PP A and B they count + or - according to the rotation.
What role does Z have to reset this count?
8 years 4 months ago #111943 by PCW
Ha! not always right and sometimes crazy wrong...
The encoder scaled position is cleared on index (Z)
( The low level count is not cleared because this would break the velocity estimation so what the hardware
does is latch the count at index and this count is scaled and used as a position offset to set the position count to 0 at index )
8 years 4 months ago #111969 by Robi63
Thank you, you are always kind
8 years 4 months ago - 8 years 4 months ago #112232 by HalaszAttila
Last edit: 8 years 4 months ago by HalaszAttila.
Time to create page: 0.348 seconds