6i25 + 7i76 not reading custom inputs

More
05 Mar 2017 19:09 #89051 by turbo
I assigned tb6 inputs 7 and 8 as tool sync and tool strobe, and I'm getting a flatline false signal for both of them on the hal scope, show, meter etc. E-stop and limit switches are functioning fine in inputs 0-3 of tb6, so I don't know why I can't get anything on those pins. Before I figured out that I could type names in the pncconfig pins I had tried to read the 7i76 pins with the same result. I am getting the expected voltages on a meter to the tb6 pin screws, which go high at 4.76V. The only differences I know of between the inputs that work and those that don't are that the working ones were drop down selections in pncconfig and running on 24v field power, whereas the nonworking ones I renamed them from unused input, and they are 5V.

Please Log in or Create an account to join the conversation.

More
05 Mar 2017 19:36 #89053 by PCW
If you have 24V field power you cannot read 5V inputs, only 24V signals

Please Log in or Create an account to join the conversation.

More
05 Mar 2017 19:44 #89054 by turbo
Shouldn't I still be able to read the voltage on the hal-scope?

Please Log in or Create an account to join the conversation.

More
05 Mar 2017 19:59 #89055 by PCW
You can read TB6 pins 1 through 4 as analog values if you select sserial mode 1 or 2
The following user(s) said Thank You: turbo

Please Log in or Create an account to join the conversation.

More
05 Mar 2017 20:12 #89057 by turbo
I haven't figured out how to change modes. I just found a sainsmart 2 channel relay module in one of my boxes so I could use that unless there is an easier way?

Please Log in or Create an account to join the conversation.

More
05 Mar 2017 20:25 #89058 by PCW
There are a couple of ways of reading 5V signals on a 7I76 if you have 24V field I/O

1. If you are not using the encoder inputs, they can be use as three 5V inputs when set to TTL mode
2. You can cheat and read the inputs 0..3 as analog values and use the "comp" component to
set a threshold value and get a boolean output

you can enable the analog inputs (and MPG inputs) by adding a "sserial_port_0=2xxx" to the config string

Please Log in or Create an account to join the conversation.