Is software Estop allowed
  • Benb
  • Benb's Avatar Topic Author
  • Premium Member
  • Premium Member
25 Aug 2024 01:49 #308571 by Benb
Is software Estop allowed was created by Benb
Software Estop in the form of UI/HMI touchscreen, flat panel display driven by mouse/keyboard, software commands (G code …) and membrane switches are NOT ALLOWED.
Control regulation rules (common sense) calls for external hardwired red mushroom push button.
Emergency stop push button must be designed to fulfill the following requirements:
  • Mushroom-head shape to make it easy to push
  • Coloured red and mounted on a bright yellow background
  • Push button must remain in latched position after it has been pushed
  • Resetting of the Estop by pulling or twisting alone shall not resume operation. A second deliberate action is needed, such as the pressing of a reset button
  • Must be located at each operator control station and at any other location where an emergency stop would be required
Now, Linuxcnc has built-in software estops (halui) and estop latch (iocontrol) these components should only used for testing and simulation. Any machine larger than coffee maker that can cause harm must be equipped with an external hardwired Estop push button and a reset button.Linuxcnc ‘gate keepers’ should warn users that - software estops are not allowed - for safety sake.The only OEM that I know uses Linuxcnc software is ‘Tormach’. If you take look at their machines, they equipped their  machines with an external hardwired Estop and reset/start push buttons, the reason liability.I am only trying to raise awareness about software estop, I am not trying to spread fear or trash Linuxcnc, to the contrary Linuxcnc is an excellent piece of software. However, Estops, safety devices and watchdogs must be built external to any controller including PLC, DCS, redundant controller …
25 Aug 2024 06:13 #308575 by Aciera
Replied by Aciera on topic Is software Estop allowed
I agree but the implementation of proper machine safety standards is first and foremost the responsibility of the machine integrator. Regulations that apply in one country may not apply in another. Also in most countries machine safety regulations will go WAY beyond having a proper emergency stop push button.
Generally I would be willing to bet with anyone building a cnc machine (other than a serious commercial company) that their machine is in breach of code somewhere.
25 Aug 2024 07:52 #308577 by rodw
Replied by rodw on topic Is software Estop allowed
There is a lot more to safety circuits than just the estop. Safety relays, redundant circuits, timers, force guided relays to name a few. Most readilly available estop buttons are not compliant to start with.  The added cost of compliancy is a few hundred dollars and few DIYers are willing to spend the money,
So yes, safety is in the hnads of the integrator.
  • Benb
  • Premium Member
  • Premium Member
25 Aug 2024 22:47 #308633 by Benb
Replied by Benb on topic Is software Estop allowed
Let me be clear ,I am only trying to raise awareness that screen estops are not allowed.
This discussion is not about machine safety relays, devices, … etc. So, let’s not mix-up things and muddy the discussion.
This awareness message is strictly about machine estop/reset only, which require very simple relay circuit. If you cannot read electrical diagrams just google start/stop circuit and you will find several examples showing realistic picture and wiring diagram for non electrical inclined.
To build an estop/reset circuit you need: red mushroom shaped push button, a push button and a relay wired as follows:
  • Moderator
  • Moderator
25 Aug 2024 23:19 #308634 by tommylight
Replied by tommylight on topic Is software Estop allowed
F117 has 9 computers with a single purpose of keeping it from falling like a brick!
Yes, it is a plane, and it is stealth.
No one asked for this info.....
Benb is trying to explain, with examples, how e-stop functions and how it should be implemented and why it is very important, so help him.
Thank you Benb.
Mentioning related stuff and the multitude of options might add to it, but it is not helping much without actual examples and corresponding info.
Another rant:
I have never used e-stop latch, although it does have it's uses for sure, but i have used the normal e-stop in and out even on 16 ton machines, as Aciera so eloquently put it "the implementation of proper machine safety standards is first and foremost the responsibility of the machine integrator" so the e-stop from LinuxCNC is just integrated into the machine e-stop system.
My point being, stop telling people to use e-stop latch unless they actually need it, they wind up wasting days trying to set it up and get frustrated, while the machines using it can be mostly stopped with a single hand and not much effort.
net e-stop-in <=== whatever-input-pin-01
net e-stop-out ===> whatever-output-pin-22
25 Aug 2024 23:33 #308635 by rodw
Not really good enough. Everything needs dual redundancy.
Note that the estop button has two redunant circuits
The main contactor needs both K1 & K2 to be triggered
K3 & K4 are seperate force guided relays. Linuxcnc is not updated with a sucessful power on unless both K3 & K4 are triggered.
Force guided relays have a non conductive pin forced between the contacts to ensure contacts cannot be welded together.
Additional safety switches eg. door switches, guards etc are placed in the S33/S34 loop with the reset button.
With such a wiring layout, it is permissable to use  linuxcnc's software power button as a reset latch. In this case, use iocontrol.0.user-request-enable as it receives a pulse to repliciate the external reset button.
BUt the safety relay cost me $250 AUD and another $100 or so for the force guided relays.
  • Benb
  • Premium Member
  • Premium Member
26 Aug 2024 02:27 #308638 by Benb
Tommy what you saying in your rant is wrong “software estop is not allowed “.   So, do yourself a favor and add an external estop to your 50 kg bench drill press and your 16-ton machine.I also hope you don’t let anyone else uses your software estop equipped machines, they are unsafe and you will not forgive yourself if someone else using them gets hurt.
And yes, no one asked me for advice but since Linuxcnc documentation does not address this subject I felt obligated to make hobbits and new Linuxcnc users aware of the use of Estop.
Tommy as Linuxcnc gate keeper do us (Linuxcnc users) favor and add a warning in the Linuxcnc documentation “software estop is not allowed.  here is no substitute for an external standalone Estop/reset”.
  • Platinum Member
  • Platinum Member
26 Aug 2024 03:21 #308643 by Cant do this anymore bye all
Replied by Cant do this anymore bye all on topic Is software Estop allowed
Gatekeeper ?
Full of good solid advice would be the better description.
Man you are so out of line with that comment.
Up til then it's been a decent discussion.
I'm just hoping there was a bit of confusion into the term "e-stop latch".
Just a little aside.
I've worked a lot of casual labour hire, disposable workers is what we really are, I was at a recycling plant, pulling steel that was missed during separation and wasn't supposed to go into the crusher. The plant wasn't the best safety wise. Anyways they had this dodgy estop setup, was like 2 step away from where you had to work. So after being there for a bit I realised the issue, spoke to the guy on site, no reaction, spoke to my contact at the labour hire mob, all they hid was ring the plant up and were assured yes there is an estop on the machine, tho access wasn't never discussed. So I said "Fuck it" and walked out. Got a call from from the labour hire mob, told them never to call again as their "safety officer was useless". Yeah and they are a major player in concrete recycling in Sydney.
So yeah machine safety is fucking important.
I fully agree a software estop is not the ideal way to go. Ah fuck I've lost my train of thought.
  • Moderator
  • Moderator
26 Aug 2024 03:35 #308647 by tommylight
Are you using translation ?
It is allowed, depends on machine, most hobby machines do not need it as the spindle is not controlled by LinuxCNC, etc etc etc
And my rant was about the "e-stop latch", not the "e-stop".
You missed the point, they do have E-stops, big ones at least two, and the proper safety stuff, always.
My small plasma machines do not have any, they do not need it, ever. My Big industrial plasma machines with DC servo motors have at least 2 e-stops and obligatory "extreme limits" on all axis
Never had a single incident on my machines, the biggest incident was braking an end mill.
I already said thank you.
Again, as Aciera said above,
26 Aug 2024 07:08 #308668 by Aciera
I don't have a problem with raising awareness about safety, there are a few post of mine on this forum where I have suggested safer procedures than what was being used. The statement I do not agree with is this one:
It's enough of a struggle to try and keep the existing code base and its documentation even halfway updated with the volunteers we have. If you would like to add information about safety then I would invite you to add to the wiki:
wiki.linuxcnc.org/cgi-bin/wiki.pl
Time to create page: 0.106 seconds
