6 years 6 months ago #162499 by Becksvill
hey clive

probably way off the mark here I am a relatively new beginner here. But i had a problem with following error when i first powered my machine up and the problem was a bug in pnconf. in the hal file the max PID error for each axis was .0005 which on a metric machine is a tiny number. just changing it to .05 meant that I had no problems.

I started reading this because I want to follow along and connect the encoders back to the control also but just thought the max error bug may have slipped under the radar..

Regards

Andrew

Please Log in to join the conversation.

More
6 years 6 months ago #164071 by Clive S

Clive S wrote:

PCW wrote: I would set Pn110,111,112,114 to their minimums and see if that improves the tracking


Peter many thanks for looking into this.

Pn109 is set for zero which I think disables Pn110,111,112 not sure if it affects 114.

But I will of course try those settings.

My Naz drives MB has failed and I am trying to get the data off the raid HD's which is going to take me some time.


Ok After setting up another machine. I have now returned to the F-error problem.

To re-cap this is a 1.8kw servo with matching drive just on the bench it does not error at 3M/min but does at 4.5M/min.You can see from the GUI that it has over shot by 1mm when it error ed
.

Attachment not found


.

Attachment not found



What do I need to adjust and in what order to sort this.

Attachment not found

Attachment not found

Please Log in to join the conversation.

More
6 years 6 months ago #164087 by PCW
You can see from the encoder velocity lagging the error that the drive has significant delay
from the command ( the commanded step rate determined mostly by FF1) and motion.
It looks like about a 20 ms delay (1/10 of a major division).

Unless this delay can be eliminated I suspect those drives will not be useful with external feedback.
(and may be a bit suspect as far as axis/axis coordination goes)

That said, is P as high as it can go without instability?
a larger amount of FF2 may also help
Plotting the commanded velocity would also help diagnosis

Please Log in to join the conversation.

More
6 years 6 months ago #164089 by Clive S
This is the manual for the drive:- www.dropbox.com/s/jp7t9hcszjcg6na/1.8Kw%...vo%20manual.pdf?dl=0

Would it be possible to put another encoder on the motor shaft or the screw and use that to close the loop !! Just a thought.

Thanks for the help.

Please Log in to join the conversation.

More
3 years 7 months ago #267684 by vre
Any progress for tuning this drive ?
Pn45-Pn50 i think are related

Please Log in to join the conversation.