Need some wiring help with board...

More
6 years 6 months ago #163274 by superlen
Ok,

After looking at the schematic, I think there are a few things I would change. (given some Assumptions I'm about to make. :) )

- A1 Your Estop is making a connection to gnd. So when you hit estop, gnd drops out and your enables feeding your drives need to go away.
- A2 - the Mesa is putting out differential for drive enables.
- The drive side is looking for active high (24v and they are enabled, gnd - they are disabled )
- The +24v on your connector is feeding Pin1 through a Resistor for the Mesa->Drive Enable. It would feed these by the same 5V that feeds the Mesa, not the 24v. The gnd for the ESTOP should be the same gnd as the 5v and the Mesas. When you hit ESTOP you lose your ground reference and the SSRs turn off.
It would work with the +24v as you have drawn, but this would require you to tie the Mesa gnd and the 24v gnd together so they have the same reference.... then you lose isolation.

- The GND you show on the right side of connector (call it pin4) should be your 24v gnd.
- Your INHs may need pullups to +24v.
- The 5V on the connector pin3 should be 24V (assuming fault signal from Drive is active low).
- I'm not up to speed on the fault input level requirements on the 7I77, but assuming it's 5v logic, so the pin4 of the SSRs that are feeding the faults needs to be referenced to the Mesa gnd.

The above is basically me trying to make your schematic an isolated design similar to the one I posted, and would be how I would tackle it. I'm sure I overlooked some stuff, but at least there are some ideas for people to digest/challenge.

Len

Please Log in to join the conversation.

More
6 years 6 months ago #163282 by Catch22

tommylight wrote: I did try to help you on the other thread when you asked for the same thing.
It is not needed, everything can be wired and work without it.
Do the drives use 5 or 24V for signalling ?
If they use 24V, you can wire the fault signal directly to 7i77 inputs, it already has enable outputs, fully isolated.
If 5V, you can still wire them directly to the first 4 inputs on the 7i77, set the board to mode 2 and add some hal logic to trigger when that input reaches 5V.[/quote


I'm sorry about that tommylight, I totally forgot about you telling me that, I'm not the sharpest nice in the drawer sometimes, as for the signalling voltage I'm not really sure, I read the documents and I would say it's 5v but not 100 % here is a couple pictures of the specs.

Attachment not found

Attachment not found

Please Log in to join the conversation.

More
6 years 6 months ago #163288 by superlen
Yossarian,

Yes, you are correct. The enables and fault output are all 5v. You don't need a 24V supply in there. I gather that's probably what John was telling you in the other thread.

Len

Please Log in to join the conversation.

More
6 years 6 months ago #163290 by Catch22
If 5V, you can still wire them directly to the first 4 inputs on the 7i77, set the board to mode 2 and add some hal logic to trigger when that input reaches 5V.
This sounds way over my head.
Where would I start looking to find out how to do this?

Please Log in to join the conversation.

More
6 years 6 months ago #163402 by tommylight
Those drives have one major issue that needs to be fixed before proceeding any further, namely the inhibit input is reversed, meaning if left unconnected the drives will be enabled, and that is a big NO for servo drives.
That can be foxed by adding a resistor to pull that input low always until Linuxcnc takes control and sends the required 5V for enabling the drives. A 1KOhm resistor should do the trick, but you will have to test that and be sure that the drives remain disabled until the enable on Linuxcnc is turned on. That input then must be connected to enable on the 7i77 for all drives separately, and the other side of the 7i77 enable connected to 5V.
The fault can be connected directly to one of the first 4 inputs on the 7i77, namely the input 0, 1, 2, 3, and those inputs should go through a comp as to trigger the fault for each axis when the input value reaches 5V, not hard to do in hal once you get the hang of it.
Do not proceed without testing the resistor part, having enable working correctly on servo driven machines is a must, there is no way around it.

Please Log in to join the conversation.

More
6 years 6 months ago #163405 by Catch22
Ok great, so do I connect the resistor to the inhibit in to the signal ground on the drive?

Please Log in to join the conversation.

More
6 years 6 months ago #163418 by tommylight

Catch22 wrote: Ok great, so do I connect the resistor to the inhibit in to the signal ground on the drive?

Yes, inhibit it and the other side of the resistor to signal GND.

Please Log in to join the conversation.

  • BeagleBrainz
  • New Member
  • New Member
More
6 years 6 months ago #163422 by BeagleBrainz
Replied by BeagleBrainz on topic Need some wiring help with board...
Your understanding of signals and grounds seems to be a but confused as you appear to be asking where to connect grounds to.

Say I two device X & Y
Each Device is Powered by a separate power supply, say X is powered by switch mode powersupply and Y is powered by a battery.
Device X has 2 terminals X_Out and X_Gnd.
Device Y has 2 terminals Y_In and Y_Gnd.

To connect Device X to Device Y:
Term X_Out ===> Y_In
Term X_Gnd ===> Y_Gnd

Without Y_Gnd & X_Gnd being connected no signal will be seen.

Now X_Gnd & Y_Gnd are common. Theoretically if Y_In needed a pull down resistor it doesn't matter if the resistor connects to X_In & X_Gnd or Y_In or Y_Gnd. Even X_in & Y_Gnd are valid. As X_In & Y_In are connected electrically and X_Gnd & Y_Gnd are also connected electrically.

Please Log in to join the conversation.

More
6 years 6 months ago #163428 by Catch22
Awesome, thanks I will do that tomorrow.

Please Log in to join the conversation.

More
6 years 6 months ago #163431 by jj80909
For AMC (Advanced Motion Controls) servo amps, you can easily invert the inhibit signal by removing a shunt soldered to the amplifier board (J1).

With J1 removed, you can wire directly to the Mesa enable - no relay(s) needed.

Jim

Please Log in to join the conversation.