2 years 8 months ago #293160 by gardenweazel
Can someone kindly verify these settings for my Durapulse GS21-23P0 please?
220V 2.2kw Spindle

 

Attachment not found



 

Attachment not found



Relevant manual pages attached.

Thanks in advance!

Thanks

Please Log in to join the conversation.

More
2 years 8 months ago #293175 by PCW
Replied by PCW on topic 7i76e to Durapulse connection
That looks correct for SINK mode, assuming you can program
DI1 to be RUN/STOP,  DI2 to be FWD/REV and frequency
command from analog 0-10V input

I think this is P3.01 = 1 and P4.00 = 2

Please Log in to join the conversation.

More
2 years 8 months ago #293177 by gardenweazel
Yes, correct.
DI1 = Digital Input 1 = FORWARD
DI2 = Digital Input 2 = REVERSE

Please Log in to join the conversation.

More
2 years 8 months ago #293178 by PCW
Replied by PCW on topic 7i76e to Durapulse connection
You need to set DI1 to RUN and DI2 to FWD/REV to work with the 7I76E
I think this is P3.01 = 1

Please Log in to join the conversation.

More
2 years 8 months ago #293181 by gardenweazel
This doesn't work and I suspect that your Parameters may be incorrect.
Manual located here .
Thanks for your feedback though.

Please Log in to join the conversation.

More
2 years 8 months ago #293183 by PCW
Replied by PCW on topic 7i76e to Durapulse connection
Ah... different GS2, this should be correct:

P00.20 = 2 Frequency command from analog input
P02.00 = 1 DI1 = RUN/STOP DI2 = FWD/REV

Please Log in to join the conversation.

More
2 years 8 months ago #293725 by gardenweazel
I am still not clear on this issue.

My spindle runs in reverse when the Durapulse VFD indicates Forward.

And I am getting an error Elo1 over voltage, likely caused by the above.

 

Attachment not found

Please Log in to join the conversation.

More
2 years 8 months ago #293728 by tommylight


My spindle runs in reverse when the Durapulse VFD indicates Forward.
Change ONLY two of the motor wires.
Do unplug the VFD before doing this.

Please Log in to join the conversation.

More
2 years 8 months ago #293743 by scotth
Elo1 over voltage is normally caused by too fast of a decel ramp or lack of a breaking resistor.

Please Log in to join the conversation.

More
2 years 8 months ago #293744 by scotth
Look at this, it may help.


P01.12 Acceleration Time 1 ♦R/W 010C 40269
P01.13 Deceleration Time 1 ♦R/W 010D 40270
P01.14 Acceleration Time 2 ♦R/W 010E 40271
P01.15 Deceleration Time 2 ♦R/W 010F 40272
P01.16 Acceleration Time 3 ♦R/W 0110 40273
P01.17 Deceleration Time 3 ♦R/W 0111 40274
P01.18 Acceleration Time 4 ♦R/W 0112 40275
P01.19 Deceleration Time 4 ♦R/W 0113 40276
P01.20 JOG Acceleration Time ♦R/W 0114 40277
P01.21 JOG Deceleration Time ♦R/W 0115 40278
Range/Units (Format: 16-bit unsigned) Default
P0145 = 0: 000–60000 sec
P0145 = 1: 00–60000 sec
1000 / 100
The acceleration time determines the time required for the AC motor drive to ramp from 0.00 Hz to
the maximum operation frequency (P01.00). The deceleration time determines the time required
for the AC motor drive to decelerate from the maximum operation frequency (P01.00) down to
0.00 Hz.
•
The acceleration and deceleration time are invalid when using P0144 Auto-acceleration and
Auto-deceleration Setting
•
Select the Acceleration/Deceleration Time 1, 2, 3, 4 with the multi-function input terminal settings
The defaults are Acceleration Time 1 and Deceleration Time 1
•
With the enabled torque limits and stall prevention functions, the actual acceleration and
deceleration time are longer than the above action time
•
Note that setting the acceleration and deceleration time too short may trigger the drive’s
protection function (P0603 Over-current Stall Prevention during Acceleration or P0601
Over-voltage Stall Prevention), and the actual acceleration and deceleration time are longer than
this setting
•
Note that setting the acceleration time too short may cause motor damage or trigger drive
protection due to over-current during the drive’s acceleration
•
Note that setting the deceleration time too short may cause motor damage or trigger drive
protection due to over-current during the drive’s deceleration or over-voltage
•
Use suitable braking resistors (refer to Appendix A: Accessories) to decelerate in a short time and
prevent over-voltage
•
When you enable P0124–P0127 (S-curve acceleration and deceleration begin and arrival time),
the actual acceleration and deceleration time are longer than the setting