hurco hawk 30 retrofit

More
5 years 5 months ago #209250 by NEMARIAZ
Replied by NEMARIAZ on topic hurco hawk 30 retrofit
Its Rotary encoder in the servo. Motor and ball screws are connected through pulley.

Please Log in to join the conversation.

More
5 years 5 months ago #209260 by PCW
Replied by PCW on topic hurco hawk 30 retrofit
Not sure what it could be other than some kind of encoder or encoder interface issue

Is the error once per turn or some specific distance between jerks?

Please Log in to join the conversation.

More
5 years 5 months ago #209285 by andypugh
Replied by andypugh on topic hurco hawk 30 retrofit
encoder.0.position might be useful too. (the "ringing' in the velocity is probably real, but the step change is suspicious.

How many encoder counts is it between jerks?

Please Log in to join the conversation.

More
5 years 5 months ago #209484 by NEMARIAZ
Replied by NEMARIAZ on topic hurco hawk 30 retrofit
Hi
One important information . Encoder ground from Yaskawa drive can not be connected to MESA encoder ground . This connection causes analogue signal to short out . I am not sure Why . So all encoder works without ground from Servo .Can this cause this?.
Any body from MESA here can throw some light.

Attachment not found



This is the encoder connection recommendation from Yaskawa

Attachment not found



Regards
Riaz

Please Log in to join the conversation.

More
5 years 5 months ago #209504 by PCW
Replied by PCW on topic hurco hawk 30 retrofit
Sounds like you have the 7I77s analog out connected to the drives ground
(input common)

Please Log in to join the conversation.

More
5 years 5 months ago #209507 by NEMARIAZ
Replied by NEMARIAZ on topic hurco hawk 30 retrofit
So shorting happens inside MESA? Card is 7i97

Please Log in to join the conversation.

More
5 years 5 months ago #209510 by PCW
Replied by PCW on topic hurco hawk 30 retrofit
Encoder ground and analog are common on the 7I97 (or 7I77)

I suspect you have the 7I97's analog output wired to the drives
input ground (which is also probably common between the
drives encoder output and analog section)

You should be able to verify this with an ohmmeter

Note that if you fix this, you will reverse the current feedback direction
so will need to change the sign of the analog output in hal

Please Log in to join the conversation.

More
5 years 5 months ago #209521 by NEMARIAZ
Replied by NEMARIAZ on topic hurco hawk 30 retrofit
That means I need to swap analog signal and ground ..and check?

Please Log in to join the conversation.

More
5 years 5 months ago #209526 by PCW
Replied by PCW on topic hurco hawk 30 retrofit
I would verify how its currently connected (with an Ohmmeter),
that is do the 7I97 AOUT pins connect the the drives input or
encoder grounds?

Please Log in to join the conversation.

More
5 years 5 months ago #209792 by NEMARIAZ
Replied by NEMARIAZ on topic hurco hawk 30 retrofit
i interchanged Analogue and GND and checked . no change in situation.
looks like some buffer circuit is required. Any suggestions?.