1 year 1 month ago #335372 by peterpan
I set configPDOS="false" and set debug level to 1 then started linuxcnc and did dmesg:
[ 5955.390588] EtherCAT DEBUG 0-3: Sync after 2916 ms: 10723 ns
[ 5955.391589] EtherCAT DEBUG 0-3: 9904 ns difference after 2920 ms.
[ 5955.391591] EtherCAT DEBUG 0-3: ref_time=812044903503955000
[ 5955.391592] EtherCAT DEBUG 0-3: app_time=812044909343879717
[ 5955.391593] EtherCAT DEBUG 0-3: start_time=812044909442878936
[ 5955.391594] EtherCAT DEBUG 0-3: cycle=1000000
[ 5955.391595] EtherCAT DEBUG 0-3: shift_time=0
[ 5955.391596] EtherCAT DEBUG 0-3: remainder=923936
[ 5955.391597] EtherCAT DEBUG 0-3: start=812044909442955000
[ 5955.391598] EtherCAT DEBUG 0-3: Setting DC cyclic operation start time to 812044909442955000.
[ 5955.393588] EtherCAT DEBUG 0-3: Setting DC AssignActivate to 0x0300.
[ 5955.396589] EtherCAT ERROR 0-3: Failed to set SAFEOP state, slave refused state change (PREOP + ERROR).
[ 5955.397588] EtherCAT ERROR 0-3: AL status message 0x001E: "Invalid input configuration".
[ 5955.399588] EtherCAT 0-3: Acknowledged state PREOP.

ethercat upload 0x60c2 1
0x02 2
ethercat upload 0x60c2 2
0xfffffffd -3

Don't know what this means; could you explain what interpolation time is?

Please Log in to join the conversation.

More
1 year 1 month ago #335401 by Hakan
It's from the ethercat manual, I put a link there a post ago.
This is unique for this servo
 

Attachment not found



You have a 1 ms cycle time in axis.ini. According to the manual you have it set to 2 ms. Change that with
Code:
ethercat download 0x60c2 1 1
and check the value again with ethercat upload.
The error comes from the drive, it thinks the config is wrong.
The only thing to do is to follow the manual.
One thing I can think of is that it doesn't like variable PDOS.
But there aren't any complains about that.
You can as a next step test to define the receive and transmit PDOS
as on page 9 and 10. Include all pdo entries even the ones you don't use.
 

Please Log in to join the conversation.

More
1 year 1 month ago #335402 by Hakan
After reading Note under the table, you can set "sync0Shift=700000" in ethercat.xml
 

Please Log in to join the conversation.

More
1 year 1 month ago #335413 by peterpan

Code:
Include all pdo entries even the ones you don't use.

Do I need to configure all pdo entries for all 7 modes? (1600 1A00, 1601 1A01, 1602 etc)

It also says the bits are unique for each operating mode; do I also need to configure the individual bits of Controlword to achieve:
"The servo must be Enabled before it can follow any command. Enable
the servo by turning on bits 1 and 2 of the Controlword (Ready to
Switch On) then turning on bits 0-3 of the Controlword (Operation
Enabled)." 
This is stated multiple times, including page 12, 13, 15 and 26

Setting "sync0Shift=700000" didn't seem to change anything that I can see

Could I just change the configuration to 2ms?


 

Please Log in to join the conversation.

More
1 year 1 month ago #335414 by Hakan
The ones on page 9 and 10 only.

The cia402 module will do the right thing with controlword and statusword, you should not need to do anything yourself.
The drive needs to be in OP first.

You can try with 2 ms, I guess. Should work too.
 

Please Log in to join the conversation.

More
1 year 1 month ago #335420 by peterpan
After adding the rest of the pdo entries on pg 9 and 10 the drive still stays in PREOP
Code:
<masters> <master idx="0" appTimePeriod="1000000" refClockSyncCycles="5"> <slave idx="0" type="EK1100" /> <slave idx="1" type="EL1008" /> <slave idx="2" type="EL2008" /> <slave idx="3" type="generic" vid="0x00000c96" pid="0x00000001" configPdos="true"> <dcConf assignActivate="300" sync0Cycle="*1" sync0Shift="700000" /> <syncManager idx="2" dir="out"> <pdo idx="1600"> <pdoEntry idx="6040" subIdx="00" bitLen="16" halPin="cia-controlword" halType="u32" /> <pdoEntry idx="6060" subIdx="00" bitLen="8" halPin="opmode" halType="s32" /> <pdoEntry idx="6071" subIdx="00" bitLen="16" halPin="target-torque" halType="s32" /> <pdoEntry idx="607A" subIdx="00" bitLen="32" halPin="target-position" halType="s32" /> <pdoEntry idx="60FE" subIdx="00" bitLen="32" halPin="digital-outputs" halType="u32" /> <pdoEntry idx="60FF" subIdx="00" bitLen="32" halPin="target-velocity" halType="s32" /> </pdo> </syncManager> <syncManager idx="3" dir="in"> <pdo idx="1a00"> <pdoEntry idx="603F" subIdx="00" bitLen="16" halPin="error-code" halType="u32" /> <pdoEntry idx="6041" subIdx="00" bitLen="16" halPin="cia-statusword" halType="u32" /> <pdoEntry idx="6061" subIdx="00" bitLen="8" halPin="opmode-display" halType="s32" /> <pdoEntry idx="6064" subIdx="00" bitLen="32" halPin="actual-position" halType="s32" /> <pdoEntry idx="606C" subIdx="00" bitLen="32" halPin="actual-velocity" halType="s32" /> <pdoEntry idx="6077" subIdx="00" bitLen="32" halPin="actual-torque" halType="s32" /> <pdoEntry idx="60F4" subIdx="00" bitLen="32" halPin="follow-error" halType="s32" /> <pdoEntry idx="60FD" subIdx="00" bitLen="32" halPin="digital-inputs" halType="u32" /> </pdo> </syncManager> </slave> </master> </masters>

The dmesg:
Code:
[100592.236726] EtherCAT DEBUG 0-3: 9936 ns difference after 400 ms. [100592.236728] EtherCAT DEBUG 0-3: ref_time=812139542737448000 [100592.236729] EtherCAT DEBUG 0-3: app_time=812139546509016167 [100592.236730] EtherCAT DEBUG 0-3: start_time=812139546609016167 [100592.236731] EtherCAT DEBUG 0-3: cycle=1000000 [100592.236732] EtherCAT DEBUG 0-3: shift_time=700000 [100592.236733] EtherCAT DEBUG 0-3: remainder=568167 [100592.236734] EtherCAT DEBUG 0-3: start=812139546610148000 [100592.236735] EtherCAT DEBUG 0-3: Setting DC cyclic operation start time to 812139546610148000. [100592.238726] EtherCAT DEBUG 0-3: Setting DC AssignActivate to 0x0300. [100592.241726] EtherCAT ERROR 0-3: Failed to set SAFEOP state, slave refused state change (PREOP + ERROR). [100592.242726] EtherCAT ERROR 0-3: AL status message 0x001E: "Invalid input configuration". [100592.244725] EtherCAT 0-3: Acknowledged state PREOP. [100592.465795] EtherCAT WARNING 0: 1 datagram UNMATCHED! [100592.489802] EtherCAT WARNING: Datagram 0000000070b69bf8 (master-fsm) was SKIPPED 1 time.

Please Log in to join the conversation.

More
1 year 1 month ago #335435 by Hakan
Change appTimePeriod as well. Lcec usually gives an error for mismatch with servoperiod, error somewhere after linuxcnc start command.
Are there any other errors in the window where you start linuxcnc?
Can you post the ouput from the "lcec_config" command?
I really only have two more ideas, try with sm sync and free run.
For sm sync change to assignActivate=100, and for free run test comment out the whole dcConf line/item.
If that doesn't makes things better I think you should hook it up to Twincat and get it going there.
 

Please Log in to join the conversation.

More
1 year 1 month ago #335462 by peterpan
This is the entirety of the linuxcnc command info
Code:
LINUXCNC - 2.9.4 Machine configuration directory is '/home/cnc/linuxcnc/configs/sim.axis' Machine configuration file is 'axis.ini' Starting LinuxCNC... linuxcnc TPMOD=tpmod HOMEMOD=homemod EMCMOT=motmod Note: Using POSIX realtime Found file(REL): ./ethercat.hal note: MAXV max: 5.000 units/sec 300.000 units/min note: LJOG max: 5.000 units/sec 300.000 units/min note: LJOG default: 0.250 units/sec 15.000 units/min note: jog_order='X' note: jog_invert=set()

When I type "lcec_config" into the command line I get command not found.

Changing dcConf didn't seem to change anything...

Is there a guide on the linuxcnc forums to setting up Twincat with LinuxCNC? I can't find out, but I could try to figure it out without one.

Please Log in to join the conversation.

More
1 year 1 month ago #335464 by peterpan
I am having trouble interpreting this thread, but it seems to have similar debug info to my problem:
forum.linuxcnc.org/ethercat/51505-new-hardware-trouble?start=0
Could my problem be EoE related?

Please Log in to join the conversation.

More
1 year 1 month ago #335494 by Hakan
I meant "lcec_configgen".
I don't think there is a guide for TwinCAT here, have not seen one.
Maybe my old stumbling tries with Twincat still works.
Youtube video Twincat start
Download TwinCAT XAE shell from beckhoff (free).
It might need other downloads as well, but once installed it seems to work.

So I think we have tried everything now.

TwinCAT should be supported by the manufacturer, so you should be able to ask the manufacturer how to get it running.
Once you have got was is needed to get the drive from PreOP+E it should be possible to replicate in lcec.
 

Please Log in to join the conversation.