Replied by peterpan on topic Trouble with Cia402 drive configuration
Hate to open this back up, but after a 2-week hiatus I came back and linuxcnc doesn't seem to start with the Clearpath drive connected. I don't recall editing anything since it was working, but I doubt that's actually possible. It might be something simple, but here's the error:
dmesg
And in the terminal running linuxcnc:
It says no such device or address about a bagillion times.
As always, thanks in advance!
dmesg
Code:
[ +0.000006] EtherCAT 0: Slave states on main device: INIT, OP.
[ +0.000002] EtherCAT 0: Re-scanning now.
[ +0.002280] EtherCAT 0: Scanning bus.
[ +1.647025] EtherCAT 0: Bus scanning completed in 1648 ms.
[ +0.000006] EtherCAT 0: Using slave 0 as DC reference clock.
[ +0.014687] EtherCAT 0: Slave states on main device: PREOP, OP.
[ +3.742316] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:07!
[ +0.000006] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003995] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:08!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.005998] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:0A!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002995] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:0B!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.005999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:0D!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:0E!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002997] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:0F!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002998] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:10!
[ +0.000003] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:11!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:12!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002993] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:13!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003003] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:14!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002994] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:15!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003000] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:16!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:17!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002997] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:18!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:19!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002995] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:1A!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:1B!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:1C!
[ +0.000005] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003988] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:1D!
[ +0.000003] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:1E!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C32:1F!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.030001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:07!
[ +0.000005] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003993] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:08!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.006996] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:0A!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.004001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:0B!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.005999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:0D!
[ +0.000003] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002992] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:0E!
[ +0.000004] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003998] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:0F!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:10!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002998] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:11!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:12!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002996] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:13!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:14!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002998] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:15!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:16!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002997] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:17!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003002] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:18!
[ +0.000005] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002991] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:19!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:1A!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002998] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:1B!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002999] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:1C!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003001] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:1D!
[ +0.000002] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.002994] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:1E!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
[ +0.003002] EtherCAT WARNING 0-0: SDO information error response while fetching SDO entry 0x1C33:1F!
[ +0.000001] EtherCAT ERROR 0-0: SDO abort message 0x06090011: "Subindex does not exist".
And in the terminal running linuxcnc:
Code:
LINUXCNC - 2.9.6
Machine configuration directory is '/home/cnc/linuxcnc/configs/sim.axis'
Machine configuration file is 'axis.ini'
Starting LinuxCNC...
linuxcnc TPMOD=tpmod HOMEMOD=homemod EMCMOT=motmod
Note: Using POSIX realtime
Found file(REL): ./ethercat.hal
Failed to execute SDO upload: Invalid argument
LCEC: slave 0.3: Failed to execute SDO upload (0x6502:0x00, error -22, abort_code 00000000)
Failed to execute SDO upload: Invalid argument
LCEC: slave 0.3: Failed to execute SDO upload (0x6060:0x00, error -22, abort_code 00000000)
Failed to execute SDO upload: Invalid argument
LCEC: slave 0.3: Failed to execute SDO upload (0x607a:0x00, error -22, abort_code 00000000)
Failed to get reference clock time: Input/output error
LCEC: slave 0.3: Failed to execute SDO upload (0x6502:0x00, error -22, abort_code 00000000)
...
Failed to get reference clock time: No such device or address
Failed to get reference clock time: Input/output error
It says no such device or address about a bagillion times.
As always, thanks in advance!
Please Log in to join the conversation.
11 months 3 weeks ago #337897
by Hakan
Replied by Hakan on topic Trouble with Cia402 drive configuration
Looks like the slaves are out of order, I mean disorder, not right numbered.
Check with "ethercat slaves" that the cia402 drive really is slave 3.
Looks to me like the Beckhoffs didn't start up properly.
Check with "ethercat slaves" that the cia402 drive really is slave 3.
Looks to me like the Beckhoffs didn't start up properly.
Please Log in to join the conversation.
11 months 3 weeks ago #337911
by peterpan
Replied by peterpan on topic Trouble with Cia402 drive configuration
You are completely correct. Do you have a clue as to why slave 3 switched to slave 0, and is there a way to force the order?
Please Log in to join the conversation.
11 months 3 weeks ago #337916
by Hakan
Replied by Hakan on topic Trouble with Cia402 drive configuration
They are numbered after the network chain. 0 is closest to the master, 1 is next, 2 is nextnext and so on .
Can't change that afaik. Rearrange the network cables if you have to have a certain numbering.
Happy it was so easy this time
Can't change that afaik. Rearrange the network cables if you have to have a certain numbering.
Happy it was so easy this time
Please Log in to join the conversation.
11 months 2 weeks ago #338145
by peterpan
Replied by peterpan on topic Trouble with Cia402 drive configuration
I have been trying to solve these problems on my own with very little headway:
When the Servo moves 2 inches, LinuxCNC registers it as ~6.5inches regardless of the encoder_scale value
joint following error when I try to jog over ~60in/min (linuxcnc units)
joint following error when try to home (probably related)
I haven't even gotten to the real configuration and am already failing :'/
Help is appreciated
When the Servo moves 2 inches, LinuxCNC registers it as ~6.5inches regardless of the encoder_scale value
joint following error when I try to jog over ~60in/min (linuxcnc units)
joint following error when try to home (probably related)
I haven't even gotten to the real configuration and am already failing :'/
Help is appreciated
Please Log in to join the conversation.
11 months 2 weeks ago #338149
by Hakan
Replied by Hakan on topic Trouble with Cia402 drive configuration
Not sure what you mean by encoder_value.
You have the cia402.x.pos-scale to work with.
Instead of mathematically figuring it out, multiply the current value with 6.5/2 = 3.25 and try again.
If you find that number matches a known relation, use that.
I think the following errors follows from the pos-scale. At least get this right first.
More text here on how to calculate pos-scale
forum.linuxcnc.org/ethercat/22346-etherc...er?start=1360#338150
You have the cia402.x.pos-scale to work with.
Instead of mathematically figuring it out, multiply the current value with 6.5/2 = 3.25 and try again.
If you find that number matches a known relation, use that.
I think the following errors follows from the pos-scale. At least get this right first.
More text here on how to calculate pos-scale
forum.linuxcnc.org/ethercat/22346-etherc...er?start=1360#338150
Please Log in to join the conversation.
11 months 2 weeks ago #338156
by peterpan
Replied by peterpan on topic Trouble with Cia402 drive configuration
Is there a good .hal tutorial you could point me towards? I'm guessing many of my problems stem from my incompetence there.
I fixed pos-scale so that linuxcnc and the drive match, but the other issues still occur. Odd thing is that it still gives the joint 0 following error at ~60in/min, despite the drive actually moving faster. I suspect, then, that I could make the drive move twice as fast and the jog error would stay at the same logical velocity.
I fixed pos-scale so that linuxcnc and the drive match, but the other issues still occur. Odd thing is that it still gives the joint 0 following error at ~60in/min, despite the drive actually moving faster. I suspect, then, that I could make the drive move twice as fast and the jog error would stay at the same logical velocity.
Please Log in to join the conversation.
11 months 2 weeks ago #338158
by peterpan
Replied by peterpan on topic Trouble with Cia402 drive configuration
I also might have stumbled upon a very similar, if not the exact same situation:
www.forum.linuxcnc.org/ethercat/56535-pi...ed-servo-in-csp-mode
www.forum.linuxcnc.org/ethercat/56535-pi...ed-servo-in-csp-mode
Please Log in to join the conversation.
11 months 2 weeks ago #338159
by Hakan
Replied by Hakan on topic Trouble with Cia402 drive configuration
Maybe there is a guide, I don't remember it right away. I mean these are, shall we say, the common problems people encounter, nothing strange about it.
I'm patient so just keep asking.
When you get following errors in EtherCAT drives at high speed there are a couple of things.
1. Tune the servo. Settings in the servo drive.
2. If you still get following error, increase FERROR and MIN_FERROR
With EtherCAT it takes two servo cycles to receive the feedback value, so feedback position
is always two cycles behind. At 60 inch/min = 1inch/sec => 0.002 inch following error due to to turn-around time.
Position feedback isn't used for anything more than to warn when it becomes too large.
Tune the servo, that is the main thing.
Answering the second post here. With the minus sign in RefClockSyncCycles value the DC and the servo loop are synchronized.
forum.linuxcnc.org/ethercat/57349-import...ration-option#335710
I'm patient so just keep asking.
When you get following errors in EtherCAT drives at high speed there are a couple of things.
1. Tune the servo. Settings in the servo drive.
2. If you still get following error, increase FERROR and MIN_FERROR
With EtherCAT it takes two servo cycles to receive the feedback value, so feedback position
is always two cycles behind. At 60 inch/min = 1inch/sec => 0.002 inch following error due to to turn-around time.
Position feedback isn't used for anything more than to warn when it becomes too large.
Tune the servo, that is the main thing.
Answering the second post here. With the minus sign in RefClockSyncCycles value the DC and the servo loop are synchronized.