- Posts: 73
- Thank you received: 0
THCAD 10 to Herocut 55i (1:1)
4 years 9 months ago #232230
by Ekholm
Replied by Ekholm on topic THCAD 10 to Herocut 55i (1:1)
Is my idea to tap into the raw voltage a bad idea, or shouldn't it work?
My thoughts it that then i would "calibrate" the voltage to be spot on?
My thoughts it that then i would "calibrate" the voltage to be spot on?
Please Log in to join the conversation.
4 years 9 months ago #232236
by rodw
Replied by rodw on topic THCAD 10 to Herocut 55i (1:1)
You don't need to calibrate the plasma, you just need to set the THCAD parameters up correctly so to rush in and change things now might be a step backwards.
lets see solve for X (volts) from thcad manual,
(x-10)/100 = 2.24 M
x-10 = 2.24m*100
x-10 = 224
x = 224+10
x =234 volts
So 10 volts in thcad = 234 volts
so your divider is 23.4:1
(234/10)
So what are the 0 volt and 10 volt numbers on your calibration sticker ?
Have you got the link on the thcad set to 1/32?
lets see solve for X (volts) from thcad manual,
(x-10)/100 = 2.24 M
x-10 = 2.24m*100
x-10 = 224
x = 224+10
x =234 volts
So 10 volts in thcad = 234 volts
so your divider is 23.4:1
(234/10)
So what are the 0 volt and 10 volt numbers on your calibration sticker ?
Have you got the link on the thcad set to 1/32?
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
4 years 9 months ago #232255
by tommylight
Replied by tommylight on topic THCAD 10 to Herocut 55i (1:1)
Do not open plasma.
The voltage does not have to be spot on, it will work even if voltage on screen is way off.
Set the scale and offset to what the calculator says, start using the machine.
If the voltage is way off, adjust the scale a bit.
The voltage does not have to be spot on, it will work even if voltage on screen is way off.
Set the scale and offset to what the calculator says, start using the machine.
If the voltage is way off, adjust the scale a bit.
Please Log in to join the conversation.
4 years 9 months ago #232271
by Ekholm
Replied by Ekholm on topic THCAD 10 to Herocut 55i (1:1)
Thanks for the help.
0v 118,2kHz
10V 938,9 kHz
Yes i have it set to 1/32.
I thought that i hade to put the scale to 2240000 :side:
0v 118,2kHz
10V 938,9 kHz
Yes i have it set to 1/32.
I thought that i hade to put the scale to 2240000 :side:
Please Log in to join the conversation.
4 years 9 months ago #232286
by rodw
Replied by rodw on topic THCAD 10 to Herocut 55i (1:1)
Ok, we will use Herz here:
Offset = 118200/32 = 3693.75
0 volt to 10 volt frequency range = 938900/32 - 3693.75
= 29340.625 - 3693.75
= 25646.875 per 10 volts
= 3564.6875 Hz per volt
But Plasmac uses volts per Hz so take the reciprocal
0.000389911051541
So your data =
offset = 3693.75
scale = 0.000389911051541
Lets do a test. Say the frequency on the encoder was 23693.75
deduct offset = 20000
THCAD internal voltage 20000 * scale = 7.798 volts
Torch voltage = max scale (234) * 7.798/10
= 182 volts
I would expect to see cut voltages of between 90-130 volts.
Its always best to take the time to understand how this works.
If you use halshow to find encoder.n.velocity when not cutting it should be hovering round the offset of 3693
Offset = 118200/32 = 3693.75
0 volt to 10 volt frequency range = 938900/32 - 3693.75
= 29340.625 - 3693.75
= 25646.875 per 10 volts
= 3564.6875 Hz per volt
But Plasmac uses volts per Hz so take the reciprocal
0.000389911051541
So your data =
offset = 3693.75
scale = 0.000389911051541
Lets do a test. Say the frequency on the encoder was 23693.75
deduct offset = 20000
THCAD internal voltage 20000 * scale = 7.798 volts
Torch voltage = max scale (234) * 7.798/10
= 182 volts
I would expect to see cut voltages of between 90-130 volts.
Its always best to take the time to understand how this works.
If you use halshow to find encoder.n.velocity when not cutting it should be hovering round the offset of 3693
Please Log in to join the conversation.
- snowgoer540
- Offline
- Platinum Member
-
Less
More
- Posts: 2580
- Thank you received: 0
4 years 9 months ago #232382
by snowgoer540
Replied by snowgoer540 on topic THCAD 10 to Herocut 55i (1:1)
To absolve some possible confusion, I feel compelled to point out there's a typo below (change red):
That's true, for a voltage divider of 1.
For a voltage divider of 23.4 (value calculated in post above), the values are as follows:
offset = 3693.75
scale = 0.00912392
Another source for the calculations: linuxcnc.org/docs/devel/html/plasma/qtpl...c.html#qt_mesa-thcad
And a handy calculator for the values: jscalc.io/calc/NTr5QDX6WgMThBVb
= 25646.875 per 10 volts
= 2564.6875 Hz per volt
But Plasmac uses volts per Hz so take the reciprocal
0.000389911051541
So your data =
offset = 3693.75
scale = 0.000389911051541
That's true, for a voltage divider of 1.
For a voltage divider of 23.4 (value calculated in post above), the values are as follows:
offset = 3693.75
scale = 0.00912392
Another source for the calculations: linuxcnc.org/docs/devel/html/plasma/qtpl...c.html#qt_mesa-thcad
And a handy calculator for the values: jscalc.io/calc/NTr5QDX6WgMThBVb
Please Log in to join the conversation.
4 years 9 months ago #232385
by rodw
Replied by rodw on topic THCAD 10 to Herocut 55i (1:1)
Thanks,
Now I know why I still scale my torch voltage with a component I wrote years before plasmac was around that does all the maths for me. I set my scale = 1 and offset = 0.
I can't quite remember the issue but very early plasmac did not let me enter the required values due to an error in the field validation limits.
0.000389911051541 * 23.4 = 0.00912392
Now I know why I still scale my torch voltage with a component I wrote years before plasmac was around that does all the maths for me. I set my scale = 1 and offset = 0.
I can't quite remember the issue but very early plasmac did not let me enter the required values due to an error in the field validation limits.
0.000389911051541 * 23.4 = 0.00912392
Please Log in to join the conversation.