yalang yl620 VFD rs485/modbus communicaiton
03 Sep 2021 08:05 #219499
by iforce2d
Replied by iforce2d on topic yalang yl620 VFD rs485/modbus communicaiton
I recently spent two days trying to get RS485 working with this VFD before giving up. It appears to be simply reject any communication on that external port no matter what settings are made. My reports in this thread might be interesting, but there's nothing good: forum.linuxcnc.org/24-hal-components/387...-rtu?start=60#218634
I would suggest just using PWM control, takes about 10 minutes to set up. If only I had a time machine...
03 Sep 2021 14:25 #219525
Replied by andypugh on topic yalang yl620 VFD rs485/modbus communicaiton
FWIW the HuangYang VFDs have the same problem, they don't actually talk modbus. The dedicated driver handles this.
It _might_ be worth trying the hy_vfd driver with this one. The worst that can happen is that you waste even more time.
04 Sep 2021 21:47 #219627
by iforce2d
I read somewhere that while the HuangYang VFDs do not talk modbus, this Yalang one actually does, and my experience with the logic analyzer and message interaction would agree. The messages it returns are well-formed modbus and consistent. The LCD control panel connection also uses standard modbus, but at a fixed baud rate (38400 in my case) that is not user-configurable. I used the logic analyzer to watch the traffic between the LCD panel and the main board, and when I imitate the panel my messages are responded to correctly, but the motor never moves.
As for the usual RS485 port, it always responds with "Illegal data value" no matter what, even when only attempting to read. I wrote a script that tried to read all registers from 0-16384 and every single one failed with the same result. It's almost like the firmware is either bugged or never intended to accept traffic on that port in the first place.
08 Sep 2021 17:34 #219981
You have probably tried this, but maybe swap the wires?
- Thank you received: 1369
15 Sep 2021 16:28 #220717
Replied by Todd Zuercher on topic yalang yl620 VFD rs485/modbus communicaiton
Does your line need termination resistors?
08 Oct 2021 14:12 #222553
by Tukbuk23
Replied by Tukbuk23 on topic yalang yl620 VFD rs485/modbus communicaiton
FYI, I got the YL620-A working on RS-485. Andypugh was right, just swap the RS-485 A/B wires. The labels (silkscreen) on the VFD PCB are incorrect.
17 Oct 2021 01:29 #223354
by mBender
Replied by mBender on topic yalang yl620 VFD rs485/modbus communicaiton
Hey, can you let me know how you got it working? I am having issues. I used vfdmod, the integrated driver, but in no way I get it working.
28 Oct 2021 15:56 #224593
by mBender
Got it working. Please see attached my files, in case someone else needs them.
28 Oct 2021 17:47 #224596
by mBender
Does anyone know what the registers for Amps, Voltage,... are in the YL 620? Or if not, how to find that out?
02 Nov 2021 12:39 #224984
I guess you could try a brute-force search looking for likely-seeming value changes.
If it isn't documented it would be difficult.Does anyone know what the registers for Amps, Voltage,... are in the YL 620? Or if not, how to find that out?
Time to create page: 0.126 seconds