09 Mar 2015 23:51 #56579
by Paul
Replied by Paul on topic M66 Wait For Arc-OK: L1 or L3?
OK - So it's not fixed or I don't see any problems on 11 gauge or thinner, but problem still there on 3/16". It just seems like the G04 P0.2 (or whatever) is sometimes being ignored. I ended up using G04 P0.6 to get through the job.
Alone, I can't watch everthing during this time, but by watching the screen's arc-ok light and listening to the torch/table, I don't think the arc-ok is faulting. Is there any suggestions of what I can check or monitor in order to better understand this problem?
Basically, it's: move to position, touch-off, lift to pierce height, fire torch, wait upto 5 seconds for arc-ok signal, wait 0.2 seconds, move Z to cut height, and cut. But sometimes when the torch fires, it's like it is going straight to cut height and moving through the lead-in without any waiting after the torch actually fires.
Any insight greatly appreciated!!
Paul
Alone, I can't watch everthing during this time, but by watching the screen's arc-ok light and listening to the torch/table, I don't think the arc-ok is faulting. Is there any suggestions of what I can check or monitor in order to better understand this problem?
Basically, it's: move to position, touch-off, lift to pierce height, fire torch, wait upto 5 seconds for arc-ok signal, wait 0.2 seconds, move Z to cut height, and cut. But sometimes when the torch fires, it's like it is going straight to cut height and moving through the lead-in without any waiting after the torch actually fires.
G00 X19.3700 Y19.7648
o<TouchOff> call
o<touchoff> sub
G38.2 Z-50 F3001.0
G10 L20 P1 Z0.000
G00 Z9.85000
G10 L20 P1 Z0.00
o<touchoff> endsub
M2
G00 Z3.8100
M03
M66 P0 L3 Q5 (Wait for ARC-OK from torch)
G04 P0.6
G01 X19.3700 Y19.7648 Z1.5240 F3810.0
Any insight greatly appreciated!!
Paul
Please Log in or Create an account to join the conversation.
19 Mar 2015 17:22 #57006
by Paul
Replied by Paul on topic M66 Wait For Arc-OK: L1 or L3?
So - It seemed to be a noise issue. At least it seems so at 65 amps. I replaced the plasma control cable with a shielded one and re-routed the torch lead and after 385 pierces all observing the coded pierce timing, I NOW feel like I have this taken care of.....Again.
Thanks for the replies.
Paul
Thanks for the replies.
Paul