Weird intermittent bug involving proximity sensors and homing

More
7 years 6 months ago #132302 by PCW
Sounds a bit more like a missing/unconnected field common/ground so as soon as you enable the drives or turn on a relay, field common is pulled up to +24V

Please Log in or Create an account to join the conversation.

More
7 years 6 months ago #132305 by Mike@CNCproCuts.com

PCW wrote: Sounds a bit more like a missing/unconnected field common/ground so as soon as you enable the drives or turn on a relay, field common is pulled up to +24V


Thanks ! Found an unconnected wire ... now everything works fine ... still don't know how it could have happened but ... that was the problem so thanks a lot for the insights ;)

Please Log in or Create an account to join the conversation.

More
7 years 6 months ago #132307 by Mike@CNCproCuts.com

andypugh wrote:

Mike@CNCproCuts.com wrote: the 7i84 inputs will have names like "hm2_5i25.0.7i84.0.0.input-00"
You should be able to find them in Halshow


I had not connected the VIN yet ... now I see it so thanks ;)

Please Log in or Create an account to join the conversation.

More
7 years 6 months ago #132437 by Mike@CNCproCuts.com
Thougt it was solved ... worked fine for 24hrs ... now the problem is back ... very strange ... could a ground loop take time to accumulate voltage ?

Please Log in or Create an account to join the conversation.

More
7 years 6 months ago - 7 years 6 months ago #132442 by Mike@CNCproCuts.com
Closing it for 30 minutes ... now it works ... intermittent ... back to square one ...
Last edit: 7 years 6 months ago by Mike@CNCproCuts.com.

Please Log in or Create an account to join the conversation.

More
7 years 6 months ago #132443 by Todd Zuercher
Sounds like a wiring problem somewhere. Check all your connections, plugs, etc. You said you found one loose connection, there could be others.