6i25 7i76 closed loop spindle
14 May 2020 07:59 #167733 by PCW
Replied by PCW on topic 6i25 7i76 closed loop spindle
What version of LinuxCNC are you using? I'm pretty sure [SPINDLE_9] has been used for a few versions
( note that for spindle control, FF0 should be 1 not FF1 )
14 May 2020 08:00 #167734 by Bob654321
Replied by Bob654321 on topic 6i25 7i76 closed loop spindle
Where would add "pid.N.maxerrorI" ? Is it replacing something? I
14 May 2020 08:12 #167739 by Bob654321
LinuxCNC 2.7.14 . (Thanks for pointing that FF0=1 not FF1) A side note I have a completely separate computer/6i25-7i76 I am using to get the spindle and tool changer up and running. I am simply unplugging from my working set up and plugging into the setup we are looking at. I am more than willing to start over from scratch if there is a version of linuxcnc that will work better for what i am doing.
14 May 2020 09:01 #167744 by PCW
I'm not sure when the spindle tuning stuff was added to calibrate. I thought is was in 2.7 but I might be wrong. You can do this by hand live halcmd in a terminal
halcmd -fk
halcmd: setp pid.s.Pgain 5
You can do this with halshow but I prefer halcmd because it has command history
(cursor keys allow you to replay/edit previous commands) and command completion
(tab key completes signal, pin, parameter, function names)
as far as the pid maxerror settings, you can do this directly in the hal file with
setp pid.s.maxerrori 123
or
setp pid.s.maxerrori [SPINDLE_9]MAX_ERROR_I
assuming you add a
MAX_ERROR_I = 123
statement in the SPINDLE_9 section of your ini file
14 May 2020 10:31 - 14 May 2020 10:34 #167755 by dgarrett
Replied by dgarrett on topic 6i25 7i76 closed loop spindle
to calibrate. I thought is was in 2.7 ...
ref: linuxcnc.org/docs/2.8/html/getting-start...bration_emccalib_tcl
commit: github.com/LinuxCNC/linuxcnc/commit/db9740e94
$ git branch --all --contains db9740e94 |grep 2\.
2.8
Last edit: 14 May 2020 10:34 by dgarrett.
14 May 2020 11:39 #167759 by PCW
Thanks dgarrett.
So spindle support in calibrate is relatively new
14 May 2020 13:25 #167768 by Bob654321
should i switch to 2.8? If it is easier to work with i can change to 2.8.
14 May 2020 15:14 #167782 by Bob654321
Maybe i am getting off track with the calibrate and 2.8 stuff. Non the less i still get the same exact behavior as I described in my initial post now with FF0 =1.
"When I mess with the spindle PID some interesting things happen. The first is when I make P higher than 1 the spindle runs faster than M3Sxx and when less than 1 spindle runs slower than M3Sxx. I can increase P slowly to a large number and the only thing that happens is spindle speed scaling. Speed oscillates slightly then settles within 5rpm no matter what value of P I use (same as if I unhook the 7i76 and hook a potentiometer to drive). If I is increased spindle speed starts about where you tell it than drifts to the maximum spindle speed. With a low I this happens slowly and with a higher I it happens faster…"
Another thing that i noticed is that a negative I will slow spindle down to 0.
Are my hal and ini files set up for my setup for closed loop? Is the above typical behavior or does it indicate a crossed wire somewhere?
14 May 2020 15:23 #167784 by PCW
Sound broken, I guess I would run open loop (FF0=1 only) and watch the PID error
pin to get some understanding of what's going on. It sounds like the encoder scaling
is way off for some reason since the PID output should drop if you are above the
setpoint and you have a non zero P or I term
BTW don't use negative PID values, the PID component has some built in assumptions
that these are positive
14 May 2020 21:57 #167804 by Bob654321
The image attached represents the pid.s.error pin with the spindle going from 0 to 2000rpm. FF0=1,everything else was 0. I would not be surprised if I made a mistake with the scale. I was a little confused when using the pncconf calculator. The encoder is a 1000 p/r differential hooked directly to the motor. Motor spins 2:1 to the spindle. Max rpm of motor/encoder=4,000rpm and spindle=8000. What would be the correct scale/ini values for the spindle?
Time to create page: 0.334 seconds