Setting pin value based on other pins
- kubes
- Thank you received: 4
31 May 2025 00:47 #329425
by kubes
Setting pin value based on other pins was created by kubes
I am using mb2hal (modbus) and it exposes a pin `mb2hal.00.00.int` that is an input, the values can be 1, 2, or 5. I need to set the values based on other bit pin:
if spindle.0.forward = true then mb2hal.00.00.in = 1
if spindle.0.reverse = true then mb2hal.00.00.in = 2
if spindle.0.on = false then mb2hal.00.00.in = 5
How do I create this logic in the hal?
- juliankoenig87
- Thank you received: 55
31 May 2025 02:00 #329426
by juliankoenig87
Replied by juliankoenig87 on topic Setting pin value based on other pins
One easy way is to use a mux8:
linuxcnc.org/docs/2.5/html/man/man9/mux8.9.html
This way you can net your three spindle signals to the three selections of the mux and you can define your modbus values to the corresponding inputs of the mux.
- Thank you received: 4154
31 May 2025 04:21 #329434
Replied by rodw on topic Setting pin value based on other pins
Look at the example in the docs for a MPG for axis selection and scaling. I think there is also a MUX4
- juliankoenig87
31 May 2025 08:01 #329441
by juliankoenig87
Yes there is a mux4. But then you will one have 2 selction bits and he needs three. Assuming there is a fourth state where nothing is active otherwise mux4 is doable I would say.
- kubes
31 May 2025 13:34 - 31 May 2025 13:36 #329460
by kubes
Replied by kubes on topic Setting pin value based on other pins
Thanks! mux4 worked.
In case others need it, here is my solution:
loadusr -Wn modbus mb2hal config=mb2hal-gt.ini
loadrt mux4 count=1
addf mux4.0 servo-thread
# esnure all is stopped! (int and float are add together and the result is sent to modbus)
setp modbus.vfd.command.int 0
setp modbus.vfd.command.float 5
# set the logic of that command to send the vdf
# 5 = stop, 1 = forward, 2 = reverse
setp mux4.0.in0 5
setp mux4.0.in1 1
setp mux4.0.in2 2
setp mux4.0.in3 5
net vfd-cmd1 mux4.0.sel0 <= spindle.0.forward
net vfd-cmd2 mux4.0.sel1 <= spindle.0.reverse
net vfd-command modbus.vfd.command.float <= mux4.0.out
net spindle-speed-fb <= modbus.vfd.status.rotation_speed.float
Last edit: 31 May 2025 13:36 by kubes.
Time to create page: 0.228 seconds