I am wiring user panel with 7i84 cards. My question: Is 7 meters(25 ft) CAT5 cable too long between Mesa 7I84 and 7I74 cards? Cable will route in energy chain along with other wires that may cause some noise(110Vac for ATC solenoids). Or is it better to keep 7i84's near 7i74 and wire panel buttons & light with 7 meter cables(about 50 wires)?
Tero
Tero
Last edit: 03 Jun 2016 07:09 by terkaa.
Please Log in or Create an account to join the conversation.
- PCW
- Away
- Moderator
Less
More
- Posts: 17899
- Thank you received: 4774
03 Jun 2016 17:18 #75446
by PCW
Replied by PCW on topic Mesa RS422 max cable length?
If the 7I84 cable is routed near switched 120VAC lines I would use shielded Cat5
Up to about 30 M is OK but the longer the parallel runs with noisy signals
the greater the chance of data errors
Up to about 30 M is OK but the longer the parallel runs with noisy signals
the greater the chance of data errors
Please Log in or Create an account to join the conversation.
- terkaa
- Offline
- Elite Member
Less
More
- Posts: 261
- Thank you received: 3
03 Jun 2016 17:41 #75450
by terkaa
Replied by terkaa on topic Mesa RS422 max cable length?
Ok, so I am good with 25ft shielded CAT6 cables?
Please Log in or Create an account to join the conversation.
- PCW
- Away
- Moderator
Less
More
- Posts: 17899
- Thank you received: 4774
03 Jun 2016 18:13 #75454
by PCW
Replied by PCW on topic Mesa RS422 max cable length?
Should be fine
Cat5E and CAT6 have the advantage of using 24 gauge wire so have lower voltage drops than CAT5