17 Nov 2017 11:22 #101923
by kibo
MESA 7i76 connect to VFD was created by kibo
Hi
can you please advise me to connect the inverter (attachment - VFD) to the 7i76 card (attachment - 7i76).
Inverter photo (Attachment - photo)
I used LinuxCNC system.
Is it correct?:
SPINDLE- => analog input COM
SPINDLE OUT => analog output AO1
SPINDLE+ => analog input AIN1
NC => ???
SPINDLE ENA- =>
SPINDLE ENA+ =>
SPINDLE DIR- => digital input X1
SPINDLE DIR+ => digital input X2
What is the +12V and COM in VFD analog input? Where from do I connect the voltage?
I'm a little confused.
Thanks a lot.
Tomas
can you please advise me to connect the inverter (attachment - VFD) to the 7i76 card (attachment - 7i76).
Inverter photo (Attachment - photo)
I used LinuxCNC system.
Is it correct?:
SPINDLE- => analog input COM
SPINDLE OUT => analog output AO1
SPINDLE+ => analog input AIN1
NC => ???
SPINDLE ENA- =>
SPINDLE ENA+ =>
SPINDLE DIR- => digital input X1
SPINDLE DIR+ => digital input X2
What is the +12V and COM in VFD analog input? Where from do I connect the voltage?
I'm a little confused.
Thanks a lot.
Tomas
Please Log in or Create an account to join the conversation.
17 Nov 2017 14:40 #101936
by PCW
Replied by PCW on topic MESA 7i76 connect to VFD
SPINDLE- => analog input COM
SPINDLE OUT => analog input AIN1
SPINDLE+ => +12V
NC => No Connection
SPINDLE ENA- => digital input COM
SPINDLE ENA+ => digital input X1
SPINDLE DIR- => digital input COM
SPINDLE DIR+ => digital input X2
If you need to run in both directions you will need to setup the VFD for "2 wire mode 2" control:
X1= ENABLE, X2 = DIR instead of the default X1 = FORWARD X2 = REVERSE
SPINDLE OUT => analog input AIN1
SPINDLE+ => +12V
NC => No Connection
SPINDLE ENA- => digital input COM
SPINDLE ENA+ => digital input X1
SPINDLE DIR- => digital input COM
SPINDLE DIR+ => digital input X2
If you need to run in both directions you will need to setup the VFD for "2 wire mode 2" control:
X1= ENABLE, X2 = DIR instead of the default X1 = FORWARD X2 = REVERSE
The following user(s) said Thank You: kibo
Please Log in or Create an account to join the conversation.
31 Dec 2017 19:28 #103908
by kibo
Replied by kibo on topic MESA 7i76 connect to VFD
Hi
I connected VFD as mentioned above. (thanks a lot PCW).
Unfortunately, I have a problem with changing the direction of the spindle.
I used Axis GUI.
I can start the spindle.
When I click to "counterclockwise" button and then to "+" and "-" it works.
But when I stop spindle and click to "clockwise" button, the spindle does not change the direction of rotation and immediately picks up the max speed.
The "+" and "-" buttons does not work in this direction.
I do not know if there is a problem with the LinuxCNC or VFD settings.
Thanks a lot and happy new year
I connected VFD as mentioned above. (thanks a lot PCW).
Unfortunately, I have a problem with changing the direction of the spindle.
I used Axis GUI.
I can start the spindle.
When I click to "counterclockwise" button and then to "+" and "-" it works.
But when I stop spindle and click to "clockwise" button, the spindle does not change the direction of rotation and immediately picks up the max speed.
The "+" and "-" buttons does not work in this direction.
I do not know if there is a problem with the LinuxCNC or VFD settings.
Thanks a lot and happy new year
Please Log in or Create an account to join the conversation.
31 Dec 2017 21:14 #103909
by PCW
Replied by PCW on topic MESA 7i76 connect to VFD
Sounds like your hal file is using the signed spindle speed pin rather than the unsigned (abs) one
can you post you hal/ini files?
can you post you hal/ini files?
The following user(s) said Thank You: kibo
Please Log in or Create an account to join the conversation.
01 Jan 2018 08:43 #103920
by kibo
Replied by kibo on topic MESA 7i76 connect to VFD
Thanks a lot.
Please Log in or Create an account to join the conversation.
01 Jan 2018 15:50 #103927
by PCW
Replied by PCW on topic MESA 7i76 connect to VFD
one problem is this:
net spindle-vel-cmd-rpm => pid.s.command
should be
net spindle-vel-cmd-rpm-abs => pid.s.command
But the spindle direction still should have changed so this suggests that in addition
to the above issue, the DIR output is not changing the VFD direction. This may be a VFD
programming issue or wiring issue
net spindle-vel-cmd-rpm => pid.s.command
should be
net spindle-vel-cmd-rpm-abs => pid.s.command
But the spindle direction still should have changed so this suggests that in addition
to the above issue, the DIR output is not changing the VFD direction. This may be a VFD
programming issue or wiring issue
The following user(s) said Thank You: kibo
Please Log in or Create an account to join the conversation.
10 Jan 2018 14:26 - 10 Jan 2018 14:27 #104237
by kibo
Replied by kibo on topic MESA 7i76 connect to VFD
Hi
I checked Wiring and VFD settings.
The problem is only when is checked "Use +- voltage for direction" in PNCconf wizard - attachment.
When I unchecked it the spindle direction works.
Now everything is working.
Thank you for your help.
I checked Wiring and VFD settings.
The problem is only when is checked "Use +- voltage for direction" in PNCconf wizard - attachment.
When I unchecked it the spindle direction works.
Now everything is working.
Thank you for your help.
Last edit: 10 Jan 2018 14:27 by kibo. Reason: Correction
Please Log in or Create an account to join the conversation.
- garrettmin
- Offline
- Senior Member
Less
More
- Posts: 60
- Thank you received: 0
04 Jul 2022 23:59 - 05 Jul 2022 00:05 #246617
by garrettmin
Replied by garrettmin on topic 7i76 + VFD A2-4007M 110V
Last edit: 05 Jul 2022 00:05 by garrettmin.
Please Log in or Create an account to join the conversation.
05 Jul 2022 00:35 #246620
by PCW
Replied by PCW on topic 7i76 + VFD A2-4007M 110V
1 SPINDLE- ==> GND
2 SPINDLE OUT ==> 5V IN
3 SPINDLE+ ==> 5V OUT
4
5 SPINDLE ENA- ==> GND
6 SPINDLE ENA+ ==> FWD
7 SPINDLE DIR- ==> Unconnected unless you need reverse
8 SPINDLE DIR+ ==>
2 SPINDLE OUT ==> 5V IN
3 SPINDLE+ ==> 5V OUT
4
5 SPINDLE ENA- ==> GND
6 SPINDLE ENA+ ==> FWD
7 SPINDLE DIR- ==> Unconnected unless you need reverse
8 SPINDLE DIR+ ==>
Please Log in or Create an account to join the conversation.
- garrettmin
- Offline
- Senior Member
Less
More
- Posts: 60
- Thank you received: 0
04 Feb 2023 20:39 - 04 Feb 2023 21:26 #263705
by garrettmin
Replied by garrettmin on topic MESA 7i76 connect to VFD
REQUEST TB4 PINOUT VERIFICATION FOR 7I76 VFD NFLIXIN 9600
7I76 TB4
1 SPINDLE- ==> ACOM
2 SPINDLE OUT ==> A1
3 SPINDLE+ ==> AM
5 SPINDLE ENA- ==> ACOM
6 SPINDLE ENA+ ==> X5 FWD
7 SPINDLE DIR- ==> X6 REV
A1 = ANALOG INPUT 10V
AM = ANALOG OUTPUT 10V
MANUAL:
nflixin.com/en/?p=217
THE VFD 9600 POWERS ON ALTHOUGH NO RESPONSE FROM SIGNALS SENT FROM 7I76 TO THE 9600 TERMINALS.
PO-00 G/P TYPE DISPLAY
1: G TYPE CONSTANT TORQUE
2: P TYPE VARIABLE LOAD
P0-01 MOTOR 1 CONTROL MODE
0 SPEED SENSORLESS VECTOR CONTROL SVC
3 VF CONTROL
P0-02 COMMAND SOURCE SELECTION (INPUT FROM BUTTONS OR DATA)
0 = PANEL BUTTONS
2 = TERMINAL CONTROL
3 = COMMUNICATION CONTROL
P0-27 BINDING COMMAND SOURCE TO FREQUENCY SOURCE
2 = A1
P5-07 AM FUNCTION SELECTION
5 = OUTPUT VOLTAGE
P4-34 SET A2 INPUT SIGNAL SELECTION
0 = VOLTAGE
1 = CURRENT SIGNAL
P0-03 MAIN FREQUENCY SOURCE (INPUT FOR SPINDLE FREQUENCY)
2 = A / 1
P8-18 STARTUP PROTECTION
0 = NO
1 = YES
P9-00 MOTOR OVERLOAD PROTECTION
0 = NO
1 = YES
P9-12 INPUT PHASE LOSS PROTECTION / CONTACTOR ENERGIZING PROTECTION SELECTION
0 = DISABLED
1 = ENABLED
P8-27 TERMINAL JOG PREFERED
0 = DISABLED
1 = ENABLED
P8-45 A1 INPUT VOLTAGE LIMIT LOWER
3.1V
ATTRIBUTE TO 0?
P8-46 A1 INPUT VOLTAGE LIMIT UPPER
P8-45 TO 3.10V
ATTRIBUTE TO 10V?
P9-47 FAULT PROTECTION #1
0 = MOTOR COAST TO STOP
P9-59 ACTION INSTANT POWER FAILURE
2 = DECELERATE TO STOP
A7-01 SELECT CONTROL MODE OF OUTPUT TERMINALS ON CONTROL BOARD
0 = CONTROL BY AC DRIVE
TEN THOUSANDS DIGIT = AM
7I76 TB4
1 SPINDLE- ==> ACOM
2 SPINDLE OUT ==> A1
3 SPINDLE+ ==> AM
5 SPINDLE ENA- ==> ACOM
6 SPINDLE ENA+ ==> X5 FWD
7 SPINDLE DIR- ==> X6 REV
A1 = ANALOG INPUT 10V
AM = ANALOG OUTPUT 10V
MANUAL:
nflixin.com/en/?p=217
THE VFD 9600 POWERS ON ALTHOUGH NO RESPONSE FROM SIGNALS SENT FROM 7I76 TO THE 9600 TERMINALS.
PO-00 G/P TYPE DISPLAY
1: G TYPE CONSTANT TORQUE
2: P TYPE VARIABLE LOAD
P0-01 MOTOR 1 CONTROL MODE
0 SPEED SENSORLESS VECTOR CONTROL SVC
3 VF CONTROL
P0-02 COMMAND SOURCE SELECTION (INPUT FROM BUTTONS OR DATA)
0 = PANEL BUTTONS
2 = TERMINAL CONTROL
3 = COMMUNICATION CONTROL
P0-27 BINDING COMMAND SOURCE TO FREQUENCY SOURCE
2 = A1
P5-07 AM FUNCTION SELECTION
5 = OUTPUT VOLTAGE
P4-34 SET A2 INPUT SIGNAL SELECTION
0 = VOLTAGE
1 = CURRENT SIGNAL
P0-03 MAIN FREQUENCY SOURCE (INPUT FOR SPINDLE FREQUENCY)
2 = A / 1
P8-18 STARTUP PROTECTION
0 = NO
1 = YES
P9-00 MOTOR OVERLOAD PROTECTION
0 = NO
1 = YES
P9-12 INPUT PHASE LOSS PROTECTION / CONTACTOR ENERGIZING PROTECTION SELECTION
0 = DISABLED
1 = ENABLED
P8-27 TERMINAL JOG PREFERED
0 = DISABLED
1 = ENABLED
P8-45 A1 INPUT VOLTAGE LIMIT LOWER
3.1V
ATTRIBUTE TO 0?
P8-46 A1 INPUT VOLTAGE LIMIT UPPER
P8-45 TO 3.10V
ATTRIBUTE TO 10V?
P9-47 FAULT PROTECTION #1
0 = MOTOR COAST TO STOP
P9-59 ACTION INSTANT POWER FAILURE
2 = DECELERATE TO STOP
A7-01 SELECT CONTROL MODE OF OUTPUT TERMINALS ON CONTROL BOARD
0 = CONTROL BY AC DRIVE
TEN THOUSANDS DIGIT = AM
Last edit: 04 Feb 2023 21:26 by garrettmin. Reason: L