Sanity Check 7i76 Spindle Connections
- bally123
- Topic Author
- Offline
- Senior Member
Less
More
- Posts: 48
- Thank you received: 5
06 Mar 2018 22:38 #107060
by bally123
Sanity Check 7i76 Spindle Connections was created by bally123
Hi,
I am planning my VSD spindle connections. I have analog sorted but grateful if someone can sanity check the Dir and Ena connections before wiring.
SPINDLE ENA-(TB4.5) > Enable drive
SPINDLE ENA+(TB4.6) > +24V from drive
SPINDLE DIR- (TB4.7) > cw/ccw drive
SPINDLE DIR- (TB4.8) > +24V from drive
*The VSD requires active high signals.
Cheers Andy
I am planning my VSD spindle connections. I have analog sorted but grateful if someone can sanity check the Dir and Ena connections before wiring.
SPINDLE ENA-(TB4.5) > Enable drive
SPINDLE ENA+(TB4.6) > +24V from drive
SPINDLE DIR- (TB4.7) > cw/ccw drive
SPINDLE DIR- (TB4.8) > +24V from drive
*The VSD requires active high signals.
Cheers Andy
Please Log in or Create an account to join the conversation.
- PCW
- Away
- Moderator
Less
More
- Posts: 17905
- Thank you received: 4774
07 Mar 2018 01:27 #107063
by PCW
Replied by PCW on topic Sanity Check 7i76 Spindle Connections
Look right to me (other than the label on TB4.8)
Please Log in or Create an account to join the conversation.
- bally123
- Topic Author
- Offline
- Senior Member
Less
More
- Posts: 48
- Thank you received: 5
07 Mar 2018 18:52 #107088
by bally123
Replied by bally123 on topic Sanity Check 7i76 Spindle Connections
Thank you.....
Andy
Andy
Please Log in or Create an account to join the conversation.
- PCW
- Away
- Moderator
Less
More
- Posts: 17905
- Thank you received: 4774
07 Mar 2018 18:59 #107090
by PCW
Replied by PCW on topic Sanity Check 7i76 Spindle Connections
The basic rule for these Optocoupler outputs is that they should work exactly like a mechanical switch
with the exception that you need to pay attention to polarity (they will be stuck ON if reversed)
and they are somewhat fragile (so if you connect them to a shorted load they will likely be damaged)
Because of the fragility its often best to test the wiring by using a mechanical switch first
with the exception that you need to pay attention to polarity (they will be stuck ON if reversed)
and they are somewhat fragile (so if you connect them to a shorted load they will likely be damaged)
Because of the fragility its often best to test the wiring by using a mechanical switch first
Please Log in or Create an account to join the conversation.
- bally123
- Topic Author
- Offline
- Senior Member
Less
More
- Posts: 48
- Thank you received: 5
07 Mar 2018 19:15 #107091
by bally123
Replied by bally123 on topic Sanity Check 7i76 Spindle Connections
That's a great explanation.... I'll be adding it as a note in my 7i76 manual.
Hopefully this helps others as much as it did me.
Hopefully this helps others as much as it did me.