Smart serial card remote error = (27) Over Current
27 Feb 2019 18:07 #127274
by cogzoid
Smart serial card remote error = (27) Over Current was created by cogzoid
We're running a 7i76e and a 7i85s daughter board to control 8 stepper axes and 10 digital outputs.
We've started to notice an odd failure that happens occasionally. Some of the digital outputs just stop working, but not all of them.
All of the digital outputs are going through relays, to protect the Mesa cards. The particular relays are these ones www.mcmaster.com/8262t11 . They have a 12mA control current, which seems completely within the capabilities of the Mesa cards. (See page 24 of www.mesanet.com/pdf/parallel/7i76eman.pdf)
We noticed this error when we added the 7i85s to the mix. (Before we had some of the motors being controlled by arduinos while we were waiting on a replacement 7i85s.)
Any things we should look at to try and figure this out?
Thanks.
We've started to notice an odd failure that happens occasionally. Some of the digital outputs just stop working, but not all of them.
All of the digital outputs are going through relays, to protect the Mesa cards. The particular relays are these ones www.mcmaster.com/8262t11 . They have a 12mA control current, which seems completely within the capabilities of the Mesa cards. (See page 24 of www.mesanet.com/pdf/parallel/7i76eman.pdf)
We noticed this error when we added the 7i85s to the mix. (Before we had some of the motors being controlled by arduinos while we were waiting on a replacement 7i85s.)
Any things we should look at to try and figure this out?
Thanks.
Please Log in or Create an account to join the conversation.
27 Feb 2019 18:13 #127275
by cogzoid
Replied by cogzoid on topic Smart serial card remote error = (27) Over Current
The errors on screen are:
hm2/hm2_7i76e.0: Smart serial card hm2/hm2_7i76e,0.7i76.0.0 remote error = (27) Over Current
hm2/hm2_7i76e,0: Smart serial card hm2/hm2_7i76e.0.7i76.0.0 remote error = (8) Remote fault
hm2/hm2_7i76e.0: Smart serial card hm2/hm2_7i76e,0.7i76.0.0 remote error = (27) Over Current
hm2/hm2_7i76e,0: Smart serial card hm2/hm2_7i76e.0.7i76.0.0 remote error = (8) Remote fault
Please Log in or Create an account to join the conversation.
27 Feb 2019 18:15 #127276
by PCW
Replied by PCW on topic Smart serial card remote error = (27) Over Current
I dont think I have seen this without an actual external fault,
so I would see if you get this error with nothing connected to the outputs
If you get this error with no loads then it indicates a 7I76E fault
a 7I85S should have no effect on this error.
When a overcurrent event is detected on an output chip, that particular
chip is disabled (so 8 will be disabled at once)
so I would see if you get this error with nothing connected to the outputs
If you get this error with no loads then it indicates a 7I76E fault
a 7I85S should have no effect on this error.
When a overcurrent event is detected on an output chip, that particular
chip is disabled (so 8 will be disabled at once)
Please Log in or Create an account to join the conversation.
27 Feb 2019 18:28 #127279
by Henk
Replied by Henk on topic Smart serial card remote error = (27) Over Current
Hi.
I have had the same problem on a 7i77 and 7i71. At first I thought it was due to faulty flyback diodes on the relays but it happened again after replacing them. I then installed a switch mode PSU for the 24v supply to the Mesa cards instead of the old transformer-rectifier ps that was in the machine.
After this one or two pins failed again but it seems to have stopped now. The machine is also at a different location now and it has not happened again.
The pins that failed as stays "on" even if lcnc is closed and pc switched off. The damage is permanent and does not reset on power-cycle.
Also, the pins that failed are individual pins, not all the pins on that header. For example 02 fails, but 00 01 03 04 etc would still be operational.
Not sure why it stopped, could it have something to do with a ground/earth connection?
Henk
I have had the same problem on a 7i77 and 7i71. At first I thought it was due to faulty flyback diodes on the relays but it happened again after replacing them. I then installed a switch mode PSU for the 24v supply to the Mesa cards instead of the old transformer-rectifier ps that was in the machine.
After this one or two pins failed again but it seems to have stopped now. The machine is also at a different location now and it has not happened again.
The pins that failed as stays "on" even if lcnc is closed and pc switched off. The damage is permanent and does not reset on power-cycle.
Also, the pins that failed are individual pins, not all the pins on that header. For example 02 fails, but 00 01 03 04 etc would still be operational.
Not sure why it stopped, could it have something to do with a ground/earth connection?
Henk
Please Log in or Create an account to join the conversation.
27 Feb 2019 18:34 #127280
by cogzoid
Replied by cogzoid on topic Smart serial card remote error = (27) Over Current
I'm trying to understand this... What would those external faults look like? A short? Something else?
Could it be caused by a voltage dip from the power supply?
So I notice no change in the 8 stepper motors being driven. However, we do notice that some, but not all of the digital outputs stop working sometimes after an error occurs. A linuxcnc restart will fix the problem.
Is there are place I can read some more on these errors so I can try and debug them?
Could it be caused by a voltage dip from the power supply?
So I notice no change in the 8 stepper motors being driven. However, we do notice that some, but not all of the digital outputs stop working sometimes after an error occurs. A linuxcnc restart will fix the problem.
Is there are place I can read some more on these errors so I can try and debug them?
Please Log in or Create an account to join the conversation.
27 Feb 2019 18:34 #127281
by PCW
Replied by PCW on topic Smart serial card remote error = (27) Over Current
If you had failures in both a 7I77 and 7I71 it does suggest a power issue of some kind
One thing to avoid is hot- plugging or switching the field power to the 7IXX board
This will cause voltage transients that can damage the output chips
One thing to avoid is hot- plugging or switching the field power to the 7IXX board
This will cause voltage transients that can damage the output chips
The following user(s) said Thank You: Henk
Please Log in or Create an account to join the conversation.
27 Feb 2019 18:41 #127282
by PCW
Replied by PCW on topic Smart serial card remote error = (27) Over Current
They could be caused by an external short or by a bad/failing output chip that has been damaged somehow
That's why I suggested disconnecting the output connectors(to see if its an internal 7I76E issue or an external issue like an intermittent short)
That's why I suggested disconnecting the output connectors(to see if its an internal 7I76E issue or an external issue like an intermittent short)
Please Log in or Create an account to join the conversation.
27 Feb 2019 21:43 #127296
by cogzoid
Replied by cogzoid on topic Smart serial card remote error = (27) Over Current
So to report back... I'm having trouble duplicating any errors. It seems things only fail when the operators are using it. I was looking over the wires again, and I did find a loose wire going to one of the relays. Perhaps this loose wire caused some intermittent problems, but it doesn't explain everything...
We're going to do some better logging so we can try to figure this out as future problems creep up.
We're going to do some better logging so we can try to figure this out as future problems creep up.
Please Log in or Create an account to join the conversation.
06 Mar 2019 20:02 #127907
by cogzoid
Replied by cogzoid on topic Smart serial card remote error = (27) Over Current
I've been doing a bunch of testing and the errors have been much less. However I did witness a remote error = (26) Over Temperature error. I'm going to add some forced ventilation and try and solve that problem.
Please Log in or Create an account to join the conversation.
11 Mar 2019 19:22 #128374
by cogzoid
Replied by cogzoid on topic Smart serial card remote error = (27) Over Current
I added a couple of fans to the cabinet. One generally exhausting the warm air, and another muffin fan pointed right at the 7i76e. We didn't see any errors after a full weekend or the robot bar pouring drinks, so I'm hopeful that we've found the solution.
Please Log in or Create an account to join the conversation.