18 May 2019 04:20 #134098 by Type_Zero_Design
Im getting my limit switrches setup here and saw this line in the 7i76e manual:

"It is suggested that inputs like limit switches use normally closed switches with one
switch leg connected to field power and the other to the 7I76E input pin,
so the normal
machine state (not at limits) is to have the inputs activated. This way, a open switch wire
or wire shorted to ground will cause a detectable machine fault. "

Obviously there is not enough space on feild I/O to connect 2 Limit switches and one home per axis. Should I just use one terminal and distribute from that?

Also running 24v with my sourcing inputs have any issues that require something special like pull up resistors.

Thanks,

Please Log in or Create an account to join the conversation.

More
18 May 2019 06:48 #134104 by pl7i92
Replied by pl7i92 on topic Some 7i76E questions
Hi
you normaly got a Case Cabinat that holds the clamp blocks witch got lots of clams on 24V
like


or like here as well
Attachments:

Please Log in or Create an account to join the conversation.

More
18 May 2019 09:47 #134141 by Mike_Eitel
Replied by Mike_Eitel on topic Some 7i76E questions
In my eyes the detailed capture of each limit switch makes only sense when you can not see the axis. Problem is that it is sometimes not easy to dasychain electronic switches. But you can to chain at least two NC sourcing ones by having vcc supplied by the signal of the first. That should work for 24v and your 7i76e. Maybe even with 4. Worth a tried if you are low with signals.
m5c
Mike

Please Log in or Create an account to join the conversation.

More
18 May 2019 11:39 - 18 May 2019 11:51 #134171 by bevins
Replied by bevins on topic Some 7i76E questions

Im getting my limit switrches setup here and saw this line in the 7i76e manual:

"It is suggested that inputs like limit switches use normally closed switches with one
switch leg connected to field power and the other to the 7I76E input pin,
so the normal
machine state (not at limits) is to have the inputs activated. This way, a open switch wire
or wire shorted to ground will cause a detectable machine fault. "

Obviously there is not enough space on feild I/O to connect 2 Limit switches and one home per axis. Should I just use one terminal and distribute from that?

Also running 24v with my sourcing inputs have any issues that require something special like pull up resistors.

Thanks,


Two limit switches for X, two limit switches for Y and one for Z(upper). Share limit switch and home. That's 3 inputs needed. Connect max and min in series Normally closed. So you always have input when not on limit, that way if wire breaks you will know.
Last edit: 18 May 2019 11:51 by bevins.

Please Log in or Create an account to join the conversation.

More
18 May 2019 11:45 #134175 by pl7i92
Replied by pl7i92 on topic Some 7i76E questions
it is the same principal as here
the cherry can take 24V easy so no need to change coltige

Please Log in or Create an account to join the conversation.

More
18 May 2019 13:22 #134182 by Type_Zero_Design
Hey guys,

Thanks for the info. Just to be clear I'm not asking about the inputs, I have plenty right now.

I was wondering about the feild power output and whether I should do something like pl7i92 suggested, and if that was going to cause any isses

Please Log in or Create an account to join the conversation.

More
18 May 2019 15:26 #134194 by pl7i92
Replied by pl7i92 on topic Some 7i76E questions
the power is the same no matter what clamp it comes from

it is always best to get on Larger mashines
Terminal blocks like 5wise for the GND and + power

as you got so many in out you need to get also some fieldpower terminals