Mesa 7i77 confirm estop

More
06 Jan 2020 14:23 #154146 by Thom
Mesa 7i77 confirm estop was created by Thom
Hi,
I am working with a Mesa 7i77.
For safety reasons I operate the mesa with a separate Field Power and logic Power (Jumper W1 is placed in the right-hand position)
If I cut off the Field Power with the emergency stop, all Outputs are low and I got the Error Message:
[qtpyvcp.plugins.notifications][ERROR]  hm2/hm2_5i25.0: Smart serial card hm2_5i25.0.7i77.0.0 
 remote error = (29) Under 
 Voltage
 (notifications.py:114)
that’s all fine!
If I reconnect the Field Power, I can control the Outputs with linuxcnc (Outputs are set in the HALSHOW)
But the Outputs are not controlled at the Mesa board.

Is there any possibility to reset the Mesa board (without closing LinuxCNC)?

Best regards,
Thom

Please Log in or Create an account to join the conversation.

More
06 Jan 2020 14:56 - 06 Jan 2020 14:57 #154148 by PCW
Replied by PCW on topic Mesa 7i77 confirm estop
You should not switch the DC 7I77 field power. If you have a specific safety related output
you should instead include it in the estop chain. If you must switch 7I77 field power
it should be done on the primary (AC) side of the field power source.

You can recover from loss of sserial communication by setting the "run" pin false and then true
Last edit: 06 Jan 2020 14:57 by PCW.
The following user(s) said Thank You: Thom

Please Log in or Create an account to join the conversation.

More
06 Jan 2020 16:18 #154150 by Thom
Replied by Thom on topic Mesa 7i77 confirm estop
Thank you very much, PCW!

You can recover from loss of sserial communication by setting the "run" pin false and then true

It works!



If you must switch 7I77 field power it should be done on the primary (AC) side of the field power source.

Ok, I thought you can use the FIELD POWER like the 1L on a Siemens SPS...?
There I learned to cut off the 24V control Voltage (for actors) with the emergency relay
All the other 24V are still in use (e.g. for sensor inputs, supply for the control, status lights, …)

Best Regards,
Thom
Attachments:

Please Log in or Create an account to join the conversation.

More
06 Jan 2020 16:40 #154153 by PCW
Replied by PCW on topic Mesa 7i77 confirm estop
There are 2 reasons you cannot switch the DC field power on a 7I77:

1. Field power supplies electronic devices with filter capacitors and switching the
DC side can cause DVDT/DIDT failures
2. The field voltage sets the input thresholds

You can switch the load power with a 7I77D (since you use 12/24V common for all loads)
And we have firmware that uses host settable thresholds so allows dropping the field voltage without error, but this is not released for the 7I77 yet (it is available for the 7I84)
The following user(s) said Thank You: Thom

Please Log in or Create an account to join the conversation.

More
06 Jan 2020 17:00 #154156 by Thom
Replied by Thom on topic Mesa 7i77 confirm estop
ok, that make sense. Thanks


2. The field voltage sets the input thresholds

just recognized that :laugh:

Please Log in or Create an account to join the conversation.

More
06 Jan 2020 22:17 - 06 Jan 2020 22:17 #154178 by bevins
Replied by bevins on topic Mesa 7i77 confirm estop

ok, that make sense. Thanks


2. The field voltage sets the input thresholds

just recognized that :laugh:


Cut the power on the output of the field power. Don't cut power feeding field power.

Use a different terminal for emerg safety switch and cut power there, so your removed the input basically.
Last edit: 06 Jan 2020 22:17 by bevins.