Hi,
I am working with a Mesa 7i77.
For safety reasons I operate the mesa with a separate Field Power and logic Power (Jumper W1 is placed in the right-hand position)
If I cut off the Field Power with the emergency stop, all Outputs are low and I got the Error Message:that’s all fine!
If I reconnect the Field Power, I can control the Outputs with linuxcnc (Outputs are set in the HALSHOW)
But the Outputs are not controlled at the Mesa board.
Is there any possibility to reset the Mesa board (without closing LinuxCNC)?
Best regards,
Thom
I am working with a Mesa 7i77.
For safety reasons I operate the mesa with a separate Field Power and logic Power (Jumper W1 is placed in the right-hand position)
If I cut off the Field Power with the emergency stop, all Outputs are low and I got the Error Message:
[qtpyvcp.plugins.notifications][ERROR] hm2/hm2_5i25.0: Smart serial card hm2_5i25.0.7i77.0.0
remote error = (29) Under
Voltage
(notifications.py:114)
If I reconnect the Field Power, I can control the Outputs with linuxcnc (Outputs are set in the HALSHOW)
But the Outputs are not controlled at the Mesa board.
Is there any possibility to reset the Mesa board (without closing LinuxCNC)?
Best regards,
Thom
Please Log in or Create an account to join the conversation.
- PCW
- Away
- Moderator
Less
More
- Posts: 17869
- Thank you received: 4776
06 Jan 2020 14:56 - 06 Jan 2020 14:57 #154148
by PCW
Replied by PCW on topic Mesa 7i77 confirm estop
You should not switch the DC 7I77 field power. If you have a specific safety related output
you should instead include it in the estop chain. If you must switch 7I77 field power
it should be done on the primary (AC) side of the field power source.
You can recover from loss of sserial communication by setting the "run" pin false and then true
you should instead include it in the estop chain. If you must switch 7I77 field power
it should be done on the primary (AC) side of the field power source.
You can recover from loss of sserial communication by setting the "run" pin false and then true
Last edit: 06 Jan 2020 14:57 by PCW.
The following user(s) said Thank You: Thom
Please Log in or Create an account to join the conversation.
- Thom
- Offline
- Junior Member
Less
More
- Posts: 25
- Thank you received: 4
06 Jan 2020 16:18 #154150
by Thom
Replied by Thom on topic Mesa 7i77 confirm estop
Thank you very much, PCW!
There I learned to cut off the 24V control Voltage (for actors) with the emergency relay
All the other 24V are still in use (e.g. for sensor inputs, supply for the control, status lights, …)
Best Regards,
Thom
It works!You can recover from loss of sserial communication by setting the "run" pin false and then true
Ok, I thought you can use the FIELD POWER like the 1L on a Siemens SPS...?If you must switch 7I77 field power it should be done on the primary (AC) side of the field power source.
There I learned to cut off the 24V control Voltage (for actors) with the emergency relay
All the other 24V are still in use (e.g. for sensor inputs, supply for the control, status lights, …)
Best Regards,
Thom
Please Log in or Create an account to join the conversation.
- PCW
- Away
- Moderator
Less
More
- Posts: 17869
- Thank you received: 4776
06 Jan 2020 16:40 #154153
by PCW
Replied by PCW on topic Mesa 7i77 confirm estop
There are 2 reasons you cannot switch the DC field power on a 7I77:
1. Field power supplies electronic devices with filter capacitors and switching the
DC side can cause DVDT/DIDT failures
2. The field voltage sets the input thresholds
You can switch the load power with a 7I77D (since you use 12/24V common for all loads)
And we have firmware that uses host settable thresholds so allows dropping the field voltage without error, but this is not released for the 7I77 yet (it is available for the 7I84)
1. Field power supplies electronic devices with filter capacitors and switching the
DC side can cause DVDT/DIDT failures
2. The field voltage sets the input thresholds
You can switch the load power with a 7I77D (since you use 12/24V common for all loads)
And we have firmware that uses host settable thresholds so allows dropping the field voltage without error, but this is not released for the 7I77 yet (it is available for the 7I84)
The following user(s) said Thank You: Thom
Please Log in or Create an account to join the conversation.
- Thom
- Offline
- Junior Member
Less
More
- Posts: 25
- Thank you received: 4
06 Jan 2020 17:00 #154156
by Thom
Replied by Thom on topic Mesa 7i77 confirm estop
ok, that make sense. Thanks
just recognized that2. The field voltage sets the input thresholds
Please Log in or Create an account to join the conversation.
- bevins
- Offline
- Platinum Member
Less
More
- Posts: 1945
- Thank you received: 335
06 Jan 2020 22:17 - 06 Jan 2020 22:17 #154178
by bevins
Cut the power on the output of the field power. Don't cut power feeding field power.
Use a different terminal for emerg safety switch and cut power there, so your removed the input basically.
Replied by bevins on topic Mesa 7i77 confirm estop
ok, that make sense. Thanks
just recognized that2. The field voltage sets the input thresholds
Cut the power on the output of the field power. Don't cut power feeding field power.
Use a different terminal for emerg safety switch and cut power there, so your removed the input basically.
Last edit: 06 Jan 2020 22:17 by bevins.
Please Log in or Create an account to join the conversation.
Moderators: PCW, jmelson
Time to create page: 0.078 seconds