7i76e vfd connection issues
6 years 8 months ago #157817 by morhaz
hello everyone,
got my 7i76e connected it to my motors and they are running. now i need to connect my vfd.
i followed the instruction in this pdf i found here
forum.linuxcnc.org/media/kunena/attachme...hluss_2017-01-02.pdf
spindle is not turning.
my vfd is SAKO SKI780
here is the manual
www.sakohz.com/download/20190124124714147.pdf
currently its programmed to recieve voltage input through AI1
D1 and D2 are forward and reverse.
thanks!!!
6 years 8 months ago #157861 by PCW
Replied by PCW on topic 7i76e vfd connection issues
You should have
+10V --> TB4 pin 3 SPIN+
AIN --> TB4 pin 2 SPINOUT
GND --> TB4 pin 1 SPIN-
DI1 --> TB4 pin 5 ENA+
GND --> TB4 pin 6 ENA-
DI2 --> TB4 pin 7 DIR+
GND --> TB4 pin 8 DIR-
Note that you would need to program your drive for RUN/DIR mode instead of
FWD/REV mode
The following user(s) said Thank You: morhaz
6 years 8 months ago #157864 by morhaz
Replied by morhaz on topic 7i76e vfd connection issues
i connected according to what you wrote.
it still isnt turning.
i have no idea what value to program for it to run in another mode.
the values for D1 and D2 are on page 22. maybe you can take a look and tell me what to program?
6 years 8 months ago - 6 years 8 months ago #157873 by PCW
I would verify that you can run the drive by putting switches from DI1 and DI2 to ground
The manual is not clear at all on how the inputs work, it has a diagram showing
the digital inputs activated by being pulled to ground, but the text seems to contradict
this and suggests that digital inputs must be pulled up to 24V to be activated
If grounding the DI inputs does not work, I would try connecting them to the drives +24V
pin and see if that activates them. If that works then I would re-wire the 7I76 ENA and DIR pins like this:
DRIVE+24 --> TB4 pin 5 ENA+
DI1 --> TB4 pin 6 ENA-
DRIVE+24 --> TB4 pin 7 DIR+
DI2 --> TB4 pin 8 DIR-
It looks like you change the mode by setting parameter P4-11 to 2 but the manual is missing any description of the modes
Last edit: 6 years 8 months ago by PCW.
6 years 8 months ago - 6 years 8 months ago #157990 by morhaz
i checked it now (was not at home yesterday) and P4-11 programmed to 0 only then grounding D1 and D2 activates the spindle. but still cant control it from linuxcnc.
edit: im adding a picture so its more clear what to connect and to where
Last edit: 6 years 8 months ago by morhaz.
6 years 8 months ago #158012 by PCW
Have you verified that the hal pin
hm2_7i76e.0.7i76.0.0.spinena
is true when you expect the spindle to be on?
Moderators: PCW, jmelson