Mesa IO switching rate
  • Tesremos
  • Tesremos's Avatar Topic Author
  • Senior Member
  • Senior Member
08 Sep 2020 10:42 #181234 by Tesremos
Mesa IO switching rate was created by Tesremos
Okay, so a quick question, Mesa 7i77
I was unable to find the information in the manual, and JT was unsure, and suggested asking.
i want to feed a tachometer (24v) into the Inputs on the field I/O to read the speed of something.
preferably with out using an encoder port(5v),
What is the maximum read rate of the Feild I/O inputs? is 1khz to fast for an accurate read?
approximate maximum pulse rate to be expected is 600hz.
any input is appreciated.
TIA
  • Moderator
  • Moderator
08 Sep 2020 11:03 #181238 by tommylight
Replied by tommylight on topic Mesa IO switching rate
Tacho's are analogue devices that produce a certain voltage at a given rotation speed, and that value is written on them, namely the voltage per 1000 rpm.
So if a tacho has written on tit that it does 24V/k that means it will output 24V at 1000 rpm, 48V at 2000 rpm and 72V at 3000 rpm.
Since you mention Hz, most probably it would be a single optical or magnetic sensor that does 1 pulse per revolution, so that will be OK to wire to Mesa inputs, and those should do about 1000 readings per second, but should be confirmed by PCW.
08 Sep 2020 17:12 #181302 by PCW
Replied by PCW on topic Mesa IO switching rate
You cannot read a 600 Hz signal with a 1 KHz servo thread,
The maximum frequency you can resolve is 1/2 of the servo thread
frequency, but this assumes perfect 50% square waves and 0 jitter
1/3 of servo thread frequency is a about that best you could expect with
~50% signals.
  • Tesremos
  • Senior Member
  • Senior Member
08 Sep 2020 21:58 #181328 by Tesremos
Replied by Tesremos on topic Mesa IO switching rate
Awesome response!
thanks very much.
ill use the encoder, :)