Mesa 5i24 recovery
- ivo
10 Jan 2021 20:46 #194777
by ivo
Mesa 5i24 recovery was created by ivo
Hi everyone,
I have a problem with 5i24_25. I managed to write errorous bitfile into card (program compillated for 25 variant but hardware set to 16). Now the card is in state when both LEDs are always on. When I tried to read out card information I get :
So after reading several threads I decided to update mesaflash to last version 3.4.1 and use recover function, but without any success. As I understand at this point card is not even capable of booting and communicating over PCI because of wrong bitfile.
After reading documentation for the card, I tried to switch card to secondary backup EEPROM (jumper W7) and was able to read IO configuration a write default bitfile.
So my question is, am I capable with starting card out of secondary EEPROM to repair/overwrite primary EEPROM ? Or should I start looking for JTAG programmer ?
If any of this sounds like nonsense, I will be glad if you correct me. At this point I have no idea what to do next.
Thanks for any suggestions.
root@debian:/home/cnc# mesaflash --device 5i24 --readhmid
No 5I24 board found
root@debian:/home/cnc# lspci -vv | grep 2718
pcilib: sysfs_read_vpd: read failed: Input/output errorSo after reading several threads I decided to update mesaflash to last version 3.4.1 and use recover function, but without any success. As I understand at this point card is not even capable of booting and communicating over PCI because of wrong bitfile.
- Thank you received: 5289
10 Jan 2021 21:23 #194782
Replied by PCW on topic Mesa 5i24 recovery
You can fix this by starting from the secondary EEPROM
and then moving the jumper to select the primary EEPROM
with the system powered up, then running mesaflash to
re-write the primary EEPROM with a working bitfile
If you corrupt both EEPROMs, you will need JTAG to recover...
BTW a safer way to try a new bitfile is to write it to the fallback area:
sudo mesaflash --device 5i24 --write test.bit --fallback
write the test bitfile into the EEPROM
sudo mesaflash --device 5i24 --reload --fallback
load the FPGA from the fallback area
If you load a bad bitfile this way, a power cycle will recover
- ivo
10 Jan 2021 21:43 - 10 Jan 2021 21:45 #194784
by ivo
Replied by ivo on topic Mesa 5i24 recovery
Thank you PCW, it worked on first try.
I read this in documentation, but was really unsure removing jumper while system is running.
Thanks also for the advice. Next time I am definitely using fallback area.
Ivo
Ivo
Last edit: 10 Jan 2021 21:45 by ivo.
Time to create page: 0.143 seconds