Assuming a 24V field voltage and conventional current flow for simplicity.
Sourcing inputs have the input common tied to +24V (so they "source" current)
They are activated by connection to ground (a sinking or NPN type sensor)
Sinking inputs have the input common tied to ground (negative of the 24V supply so they "sink current)
They are activated by connection to +24V (a sourcing or PNP type sensor)
A sinking sensor must be matched with a sourcing input and vice-versa.
Sourcing inputs have the input common tied to +24V (so they "source" current)
They are activated by connection to ground (a sinking or NPN type sensor)
Sinking inputs have the input common tied to ground (negative of the 24V supply so they "sink current)
They are activated by connection to +24V (a sourcing or PNP type sensor)
A sinking sensor must be matched with a sourcing input and vice-versa.
Last edit: 05 Oct 2022 18:28 by PCW. Reason: clarify
The following user(s) said Thank You: sk_linuxcnc
Please Log in or Create an account to join the conversation.
- arvidb
-
- Offline
- Platinum Member
-
Less
More
- Posts: 459
- Thank you received: 158
05 Oct 2022 18:37 #253556
by arvidb
Replied by arvidb on topic Mesa 7i96 mixed voltage field input wiring
Attachments:
The following user(s) said Thank You: sk_linuxcnc
Please Log in or Create an account to join the conversation.
- blazini36
- Offline
- Platinum Member
-
Less
More
- Posts: 972
- Thank you received: 167
05 Oct 2022 19:06 - 05 Oct 2022 19:18 #253561
by blazini36
Replied by blazini36 on topic Mesa 7i96 mixed voltage field input wiring
Edit: cuz PCW's 100% right. A brain fart had me spun around on sinking and sourcing.
I will say that the comment about the manual section is a bit misleading. The case of a PNP switch doesn't imply that switches have a common positive, just a "less positive" reference. not sure that saying a "negative reference" is correct to say.
I will say that the comment about the manual section is a bit misleading. The case of a PNP switch doesn't imply that switches have a common positive, just a "less positive" reference. not sure that saying a "negative reference" is correct to say.
Last edit: 05 Oct 2022 19:18 by blazini36.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18115
- Thank you received: 5334
05 Oct 2022 19:25 - 05 Oct 2022 19:26 #253564
by PCW
Replied by PCW on topic Mesa 7i96 mixed voltage field input wiring
The issue is that ground is common for sinking inputs but the + voltage is the reference
for sourcing inputs.
With sourcing inputs, when you have contacts or NPN sensors,
having a common say 24V reference is fine (since the inputs will
swing the full 24V) but they will not work with 5V outputs (say a MPG).
I guess you could use a 5V common but that is marginal with switches
and NPN sensors with indicators (which have a built in pullup to 24V)
With sinking inputs you have none of these issues with mixed voltages.
for sourcing inputs.
With sourcing inputs, when you have contacts or NPN sensors,
having a common say 24V reference is fine (since the inputs will
swing the full 24V) but they will not work with 5V outputs (say a MPG).
I guess you could use a 5V common but that is marginal with switches
and NPN sensors with indicators (which have a built in pullup to 24V)
With sinking inputs you have none of these issues with mixed voltages.
Last edit: 05 Oct 2022 19:26 by PCW. Reason: format/clarify
Please Log in or Create an account to join the conversation.
- blazini36
- Offline
- Platinum Member
-
Less
More
- Posts: 972
- Thank you received: 167
05 Oct 2022 19:32 - 05 Oct 2022 19:44 #253567
by blazini36
Replied by blazini36 on topic Mesa 7i96 mixed voltage field input wiring
No, once you corrected me in typical PCW fashion I realized you were right on both accounts. Trying to fix my brain to say "sourcing" for positive is gonna be a challenge.....I've been saying it wrong for years lol.
But that's what I mean about the manual page, it pretty much says the same thing thing for NPN and PNP where it is correct for NPN but PNP the sensors just have to be more positive than the input common pin, not that they need to be connected as a common positive between each other.
A negative (ie -15v) input common would be a really tricky thing to explain when the positive input would be the 0v common of other things in the box.
But that's what I mean about the manual page, it pretty much says the same thing thing for NPN and PNP where it is correct for NPN but PNP the sensors just have to be more positive than the input common pin, not that they need to be connected as a common positive between each other.
A negative (ie -15v) input common would be a really tricky thing to explain when the positive input would be the 0v common of other things in the box.
Last edit: 05 Oct 2022 19:44 by blazini36.
The following user(s) said Thank You: tommylight
Please Log in or Create an account to join the conversation.
- Pipik
- Offline
- New Member
-
Less
More
- Posts: 13
- Thank you received: 3
05 Mar 2025 12:37 #323255
by Pipik
Replied by Pipik on topic Mesa 7i96 mixed voltage field input wiring
PCW, how do you solved that inputs can source and sink (depends on one comm pin voltage/ground) and also can source/sink 5-36V range? I am definitely not master electronic engineer like you, but need to solve a simmilar issue. Some schematic?
Thank you.
Thank you.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18115
- Thank you received: 5334
05 Mar 2025 14:33 #323272
by PCW
Replied by PCW on topic Mesa 7i96 mixed voltage field input wiring
Typically you can only use mixed voltages with sinking inputs (input common grounded)
In this case, any positive input voltage from +5V to +36V will be detected by the 7I96
isolated inputs.
In this case, any positive input voltage from +5V to +36V will be detected by the 7I96
isolated inputs.
The following user(s) said Thank You: sk_linuxcnc
Please Log in or Create an account to join the conversation.
- Pipik
- Offline
- New Member
-
Less
More
- Posts: 13
- Thank you received: 3
05 Mar 2025 14:49 #323275
by Pipik
Replied by Pipik on topic Mesa 7i96 mixed voltage field input wiring
I get the general principle of inputs in your MESA cards, I understood. You have made a very simple and easily understable manuals with you cards, btw.
But I am trying to solve simmilar inputs possibilities in one of my arduino wirings. I would like to have a little universal solution like you have on 7i96 cards, not just TTL as usual, but cant figure out what parts is best to use to achieve this.
But I am trying to solve simmilar inputs possibilities in one of my arduino wirings. I would like to have a little universal solution like you have on 7i96 cards, not just TTL as usual, but cant figure out what parts is best to use to achieve this.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18115
- Thank you received: 5334
05 Mar 2025 16:10 #323283
by PCW
Replied by PCW on topic Mesa 7i96 mixed voltage field input wiring
Here is the 7I96/7I96S input circuit
Notes:
1. The quad optos are AC input type
2. The solid GND symbol is input common
Notes:
1. The quad optos are AC input type
2. The solid GND symbol is input common
Attachments:
The following user(s) said Thank You: tommylight, Pipik
Please Log in or Create an account to join the conversation.
- alexandrap
- Offline
- Junior Member
-
Less
More
- Posts: 22
- Thank you received: 2
27 Jul 2025 05:26 - 27 Jul 2025 05:31 #332398
by alexandrap
Replied by alexandrap on topic Mesa 7i96 mixed voltage field input wiring
1.)Hello,Is this connection of the 7i96 inputs identical / similar for the 7i95T?
2.)What is the connection diagram for MPG ENCODER INPUTS (7i95T)?
I have a problem - in the manual for the 7i95T (page 17) it says:
" MPG ENCODER INPUTS
Standard 7I95 firmware provides 4 quadrature MPG encoder inputs on isolated
inputs 0 through 7. Since the input threshold on isolated inputs is about 3V, its best to use
sinking inputs (with the input common terminal tied to +5V) with TTL output level MPGs."
Isn't that sourcing input?
Thanx
2.)What is the connection diagram for MPG ENCODER INPUTS (7i95T)?
I have a problem - in the manual for the 7i95T (page 17) it says:
" MPG ENCODER INPUTS
Standard 7I95 firmware provides 4 quadrature MPG encoder inputs on isolated
inputs 0 through 7. Since the input threshold on isolated inputs is about 3V, its best to use
sinking inputs (with the input common terminal tied to +5V) with TTL output level MPGs."
Isn't that sourcing input?