My machine has four IHSV57 servos connected to a MESA 7i76, on connector TB2. Each of the servos has Alarm+ and Alarm-, as well as Ena+ and Ena-.
How can I wire those to the 7i76? Can Alarm+- drive the digital inputs? Can Ena+- be set using digital outputs?
Last edit: 15 Dec 2022 23:53 by knipknap.
- Thank you received: 5334
15 Dec 2022 23:53 #259598
Replied by PCW on topic How to connect Alarm and Enable on 7i76 boards
Yes, the IHSV57 enable input and alarm outputs are compatible with
the 7I76 I/O:
+24V --> Alarm+
Alarm- --> 7I76 input
7I76 output --> Ena+
Ena- --> GND
Note that you can parallel all 4 enables so they are all enabled at once
7I76 output --> Ena0+,Ena1+,Ena2+,Ena3+
Ena0-,Ena1-,Ena2-,Ena3- --> GND
Likewise, you can parallel the alarms if you don't need to know which axis
has a fault:
+24V --> Alarm0+,Alarm1+,Alarm2+,Alarm3+
Alarm0-,Alarm1-,Alarm2-,Alarm3- --> 7I76 input
the 7I76 I/O:
+24V --> Alarm+
Ena- --> GND
has a fault:
- knipknap
16 Dec 2022 00:36 #259599
by knipknap
Replied by knipknap on topic How to connect Alarm and Enable on 7i76 boards
Fantastic, thank you for the quick reply! That helps, I will wire it that way.
- Thank you received: 4152
16 Dec 2022 05:12 #259610
Replied by rodw on topic How to connect Alarm and Enable on 7i76 boards
Note in hal, the alarms go to joint.N.amp-fault-in
Also the enableterminals on the drive, usually do the opposite and disable the motors so they need to be enabled on an estop, not on startup.