Help with Busellato JET 2 spindle retrofit – VFD overload
- GDTH
-
Topic Author
- Away
- Senior Member
-
Less
More
- Posts: 45
- Thank you received: 2
27 Aug 2025 07:33 #333977
by GDTH
Help with Busellato JET 2 spindle retrofit – VFD overload was created by GDTH
Hi all,I’m in the process of retrofitting a Busellato JET 2 CNC machine. The machine has one main spindle, a side spindle, and drills, but I only need to control the main spindle.The spindle is still running on the original VFD, which has not been altered or replaced.Originally, the VFD was controlled via serial communication, but since I’m using a Mesa 7i77 card, I converted it to 0–10 V analog control (the serial setup seemed unnecessarily complex and hard to understand).Here’s what I’ve tried so far:
Omron F7 guide
Omron F7 full manual
- Using the original VFD (unchanged).
- Converted VFD control from serial → 0–10 V (Mesa 7i77).
- Adjusted VFD parameters to allow external analog speed control.
- Able to start the spindle successfully.
- Spindle ramps up but only reaches ~50 Hz.
- After about 10 seconds at 50 Hz, the VFD trips into overload.
- It sounds like the spindle wants to accelerate further but is somehow being held back.
- I’ve spent several hours tweaking and checking parameters, but I can’t figure out where it’s going wrong.
Omron F7 guide
Omron F7 full manual
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 23475
- Thank you received: 4994
27 Aug 2025 13:27 #333991
by andypugh
Replied by andypugh on topic Help with Busellato JET 2 spindle retrofit – VFD overload
The VFD on my high-speed spindle feels a bit like this, it starts sluggishly then seems to nearly get stuck, but in my case it then accelerates away to commanded speed.
Make sure that you really are getting 10V (or whatever) on the analogue voltage input to the VFD using a multimeter. (Also check the polarity...)
You could try operating the VFD with a potentiometer in the conventional way to check if the behaviour is the same.
Make sure that you really are getting 10V (or whatever) on the analogue voltage input to the VFD using a multimeter. (Also check the polarity...)
You could try operating the VFD with a potentiometer in the conventional way to check if the behaviour is the same.
Please Log in or Create an account to join the conversation.
- GDTH
-
Topic Author
- Away
- Senior Member
-
Less
More
- Posts: 45
- Thank you received: 2
27 Aug 2025 20:04 #334004
by GDTH
Replied by GDTH on topic Help with Busellato JET 2 spindle retrofit – VFD overload
ah okay, i will take a poteniometer with me next time. the machine is not close by. are there other things you might suggest? i was thinking of maybe doing the auto tune with the vfd, if i can figure it out.
Do you also think that i force it too quickly to high freq or just too slow?
Also a picture of the spindle, in case it helps some insight
Do you also think that i force it too quickly to high freq or just too slow?
Also a picture of the spindle, in case it helps some insight
Please Log in or Create an account to join the conversation.
- jmelson
- Offline
- Moderator
-
Less
More
- Posts: 826
- Thank you received: 160
27 Aug 2025 20:16 #334005
by jmelson
Jon
Replied by jmelson on topic Help with Busellato JET 2 spindle retrofit – VFD overload
Yes, it might solve the problem if you add a limit3 (I think that is the name of the hal component) to slow down the change of the spindle speed value.ah okay, i will take a poteniometer with me next time. the machine is not close by. are there other things you might suggest? i was thinking of maybe doing the auto tune with the vfd, if i can figure it out.
Do you also think that i force it too quickly to high freq or just too slow?
Also a picture of the spindle, in case it helps some insight
Jon
The following user(s) said Thank You: tommylight
Please Log in or Create an account to join the conversation.
Moderators: PCW, jmelson
Time to create page: 0.061 seconds