5 years 8 months ago #197691 by PCW
Replied by PCW on topic Another Elumatec SBZ130
I would first verify expected analog outputs with the analog
outputs disconnected from the drives. Low outputs could
be caused by a PID parameter, hal connection, or wiring error
The following user(s) said Thank You: Benno

Please Log in or Create an account to join the conversation.

More
5 years 8 months ago #197769 by Benno
Replied by Benno on topic Another Elumatec SBZ130
Hello PCW,
Thank you for your help. I found a small difference between the other axes and the x-axis:
Code:
net y-vel-cmd => pid.y.command-deriv
(also for z, u)
After I commented out the line, everything moved nicely :-) but still not calibrated.
I'll try the long x axis next week.:unsure:
Also a big thank you to Tom
The following user(s) said Thank You: tommylight

Please Log in or Create an account to join the conversation.

More
5 years 8 months ago #197773 by tommylight
Replied by tommylight on topic Another Elumatec SBZ130
Sorry, was out of order, messed up my eyes pretty badly 2 days ago.
Those lines were omitted for some testing and forgot to enable them again.

Please Log in or Create an account to join the conversation.

More
5 years 8 months ago #197784 by Benno
Replied by Benno on topic Another Elumatec SBZ130
I'm sorry to hear that. I hope you get well soon!

Please Log in or Create an account to join the conversation.