Spindle will not stay running
1 year 6 months ago #326650 by PCW
Replied by PCW on topic Spindle will not stay running
Looking at the hal file, I would suspect the estop input so you might try adding:
setp hm2_7i96s.0.inm.00.input-06-slow true
(the noise may also affect the other inputs so you might try with all)
1 year 6 months ago #326651 by Jabbery
Yes. I don't always trust over seas items so even if they don't have a ground lug they are grounded. All wire has grounded drains, 7i96s frame ground, emi filter, spindle, machine frame, stepper drivers are all grounded to earth ground
1 year 6 months ago #326662 by Jabbery
ok there is a freight train at the end of the tunnel!
It worked sort of. Not stable but it did show what is happening.
I put the setp on all inputs.
The EStop I now see toggles which it should not. The EStop is not actually wired yet and will be normally closed so there is always a 24V. Would this stop noise? The limits send 24V when detected but the spindle is not running. Will a limit triggering while operating cause any issue?
1 year 6 months ago #326663 by PCW
Yes, limits triggering will also cause a fault and change to machine-off state.
Maybe a wiring issue with the input common, or just limits/estop wired
near power signals.
1 year 6 months ago #326665 by Jabbery
Found another problem that seems to have fixed it. The machine is manufactured in the east, the input switches/buttons go through a wide metal clamp that I assumed was frame grounding the shielding of the wire, it was not. When I earth grounded the shield with the setp suggestion the random EStop trip seems to have stopped. It will take more tests to be sure.
Input common is Negative on the 24v PS. Limit switches are inductive and signal 24v when tripped, EStop will be 24V normal, 0V when triggered.
Time to create page: 0.298 seconds