PnCConf pid loop wiring error
- Thank you received: 5280
17 Aug 2012 14:46 - 17 Aug 2012 14:49 #23340
PnCConf pid loop wiring error was created by PCW
There appears to b a connection/signal name problem at least with the 7I77 and maybe
all PID loops that use encoders and the PID comp:
The the encoder velocity pin connects to PID comps command-deriv pin
instead of the feedback-deriv pin as it should.
This was caught by Todd Zuercher:
www.linuxcnc.org/index.php/english/compo...ew&catid=10&id=23211
Last edit: 17 Aug 2012 14:49 by PCW.
- Thank you received: 2162
18 Aug 2012 01:11 #23375
Replied by cmorley on topic Re:PnCConf pid loop wiring error
This would have affected virtually all servo systems in 2.5 from PNCconf.
I have fixed the name from commanded to feedback (oops!)
just so I'm clear feedback-deriv should be connected to encoder.velocity
and x-vel-fb makes sense for the signal name.
Chris M
Chris M
18 Aug 2012 03:26 #23376
Replied by PCW on topic Re:PnCConf pid loop wiring error
Yes, PID.n.feeback-deriv connects to encoder.n.velocity (or resolver.n.velocity)
PID.n.command-deriv should probably be left unconnected
18 Aug 2012 05:35 #23378
Thanks Peter. I pushed the fix.
Time to create page: 0.049 seconds