configuring estop_latch
17 Nov 2012 02:53 #26685
by sliptonic
configuring estop_latch was created by sliptonic
I have a 5i25/7i77 combo that I'm using in a retrofit bridgeport clone. I'd like to implement the estop circuit like in example 4: wiki.linuxcnc.org/cgi-bin/wiki.pl?Sample_HAL_And_ClassicLadder
I'm told that the estop_latch component works this way. I'm trying to understand how to make this work through pncconf without hand editing the main .hal file.
I've added the following to my custom.hal file but since iocontrol.0.emc-enable-in is already linked to estop-out it fails. Any suggestions?
# estop
loadrt estop_latch
addf estop-latch.0 servo-thread
net estop-loopout iocontrol.0.emc-enable-in <= estop-latch.0.ok-out
net estop-loopin iocontrol.0.user-enable-out => estop-latch.0.ok-in
net estop-reset iocontrol.0.user-request-enable => estop-latch.0.reset
net remote-estop estop-latch.0.fault-in <= hm2_5i25.0.7i77.0.0.input-00-not
I'm told that the estop_latch component works this way. I'm trying to understand how to make this work through pncconf without hand editing the main .hal file.
I've added the following to my custom.hal file but since iocontrol.0.emc-enable-in is already linked to estop-out it fails. Any suggestions?
# estop
loadrt estop_latch
addf estop-latch.0 servo-thread
net estop-loopout iocontrol.0.emc-enable-in <= estop-latch.0.ok-out
net estop-loopin iocontrol.0.user-enable-out => estop-latch.0.ok-in
net estop-reset iocontrol.0.user-request-enable => estop-latch.0.reset
net remote-estop estop-latch.0.fault-in <= hm2_5i25.0.7i77.0.0.input-00-not
Please Log in or Create an account to join the conversation.
17 Nov 2012 04:07 - 17 Nov 2012 04:09 #26686
by BigJohnT
Replied by BigJohnT on topic configuring estop_latch
unlinkp them first (above the net estop... lines).
linuxcnc.org/docs/html/hal/basic_hal.html#_unlinkp
John
linuxcnc.org/docs/html/hal/basic_hal.html#_unlinkp
John
Last edit: 17 Nov 2012 04:09 by BigJohnT.
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
Less
More
- Posts: 5007
- Thank you received: 1441
17 Nov 2012 09:51 #26694
by Todd Zuercher
Replied by Todd Zuercher on topic configuring estop_latch
Here is how I did it with my 5i25-7i77 set up. I did use pnc config but I don't remember if I modified this part by hand. I think I did change something but I can't remember what.
net estop-out hm2_5i25.0.7i77.0.0.output-02
net estop-ext <= hm2_5i25.0.7i77.0.0.input-14
net estop-out <= iocontrol.0.user-enable-out
net estop-ext => iocontrol.0.emc-enable-in
I ran the wire from the above 7i77output to my e-stop switches, then on the other side of the e-stop chain, I connected 2 wires one that went back to the above 7i77 input, and the other one to a series of relays and contractors that shut off every thing I wanted turned off. This might not be the right/best way, but it is working well for me.
net estop-out hm2_5i25.0.7i77.0.0.output-02
net estop-ext <= hm2_5i25.0.7i77.0.0.input-14
net estop-out <= iocontrol.0.user-enable-out
net estop-ext => iocontrol.0.emc-enable-in
I ran the wire from the above 7i77output to my e-stop switches, then on the other side of the e-stop chain, I connected 2 wires one that went back to the above 7i77 input, and the other one to a series of relays and contractors that shut off every thing I wanted turned off. This might not be the right/best way, but it is working well for me.
Please Log in or Create an account to join the conversation.
17 Nov 2012 12:44 - 17 Nov 2012 12:44 #26698
by cmorley
Replied by cmorley on topic configuring estop_latch
To use PNCconf to do this
on the advanced page select include classicladder PLC
check the estop program
make sure the include hal connections is selected.
You must select a input signal on the mesa page for this program.
select an input pin and select external control estop-in
and that should be it. when that input is false estop is on.
That page you referenced is VERY out of date (it actually says that) but the ladder program is the same.
Chris M
on the advanced page select include classicladder PLC
check the estop program
make sure the include hal connections is selected.
You must select a input signal on the mesa page for this program.
select an input pin and select external control estop-in
and that should be it. when that input is false estop is on.
That page you referenced is VERY out of date (it actually says that) but the ladder program is the same.
Chris M
Last edit: 17 Nov 2012 12:44 by cmorley.
Please Log in or Create an account to join the conversation.
17 Nov 2012 21:14 - 17 Nov 2012 21:15 #26707
by BigJohnT
Replied by BigJohnT on topic configuring estop_latch
Chris,
Did you see the estop_latch component thread? It does the same thing but without classicladder.
linuxcnc.org/index.php/english/forum/47-...5861-external-e-stop
John
Did you see the estop_latch component thread? It does the same thing but without classicladder.
linuxcnc.org/index.php/english/forum/47-...5861-external-e-stop
John
Last edit: 17 Nov 2012 21:15 by BigJohnT.
Please Log in or Create an account to join the conversation.
18 Nov 2012 11:48 #26736
by cmorley
Replied by cmorley on topic configuring estop_latch
No I hadn't - I'm behind the times
Please Log in or Create an account to join the conversation.
Moderators: cmorley