5i25 w/7i76 external estop setup question

More
05 Mar 2014 15:53 - 05 Mar 2014 23:42 #44426 by b2unit
there's 2 port in physical estop button one is connected ground of power supply
and another one is connected input0 in 7i76.
I set hal file for external estop. as I know nothing to do with more..
I dont know what is wrong..
when I launched linuxcnc I couldn't change estop button status in left top of the program window.
please have look at my hal file and give me some advice for this situation.

thanks,
Byoungil

File Attachment:

File Name: CNC_D525MW.hal
File Size:7 KB
Attachments:
Last edit: 05 Mar 2014 23:42 by b2unit.

Please Log in or Create an account to join the conversation.

More
05 Mar 2014 21:22 #44437 by cncbasher
what type of switch are you using ? , is it a nc type ( normaly closed contact )
as this is an estop the convention is to use a nc switch

remove the -not as it does not need to be inverted
The following user(s) said Thank You: b2unit

Please Log in or Create an account to join the conversation.

More
05 Mar 2014 22:37 #44442 by PCW
Actually for a NC switch the 7I76 input pin should be inverted,
but you must supply +voltage to the 7I76 input so

+24V --> NC Estop switch pin 1 --> NC Estop switch pin 2 --> 7I76input and other hardware that should be disabled by estop

With this setup , the normal situation is that the 7I76 input is high but goes low on estop so the inverted pin is needed
The following user(s) said Thank You: b2unit

Please Log in or Create an account to join the conversation.

More
05 Mar 2014 23:38 #44443 by b2unit
thanks a lot!
for my clear understanding..like this diagram right?


Attachments:

Please Log in or Create an account to join the conversation.

More
05 Mar 2014 23:44 #44445 by PCW
Thats right, though the blue wire may go to other hardware estop logic

Please Log in or Create an account to join the conversation.

More
06 Mar 2014 00:20 #44447 by b2unit
what's the meaning of other hardware estop logic?
sorry for taking your time..please explain more with example.

thanks,
Byoungil Choi

Please Log in or Create an account to join the conversation.

More
06 Mar 2014 00:32 #44448 by PCW
For example the blue wire might go to a relay that removes power from axis drives/spindle
when the estop button is hit

(note that if a relay coil and 7I76 input are connected the relay coil must have a flyback diode to prevent high voltage spikes)
The following user(s) said Thank You: b2unit

Please Log in or Create an account to join the conversation.