19 Jul 2014 23:43 #48944
by andypugh
I would hazard a guess that you want count-enable false and direct-value true but the docs are not clear, so you might need to try both.
Your analogue input is likely to be a float. halui.feed-override.counts is an s32 (signed 32 bit integer) so you need to use:
www.linuxcnc.org/docs/html/man/man9/conv_float_s32.9.html
And, even though it is only a type conversion, it needs to be loadrt-ed, and addf-ed or it won't do anything.
Replied by andypugh on topic Very basic Pnconf questions - daughter boards
net floatout.pin => halui.feed-override.counts setp halui.feed-override.count-enable true setp halui.feed-override.direct-value true setp halui.feed-override.scale 0.1
I would hazard a guess that you want count-enable false and direct-value true but the docs are not clear, so you might need to try both.
Your analogue input is likely to be a float. halui.feed-override.counts is an s32 (signed 32 bit integer) so you need to use:
www.linuxcnc.org/docs/html/man/man9/conv_float_s32.9.html
And, even though it is only a type conversion, it needs to be loadrt-ed, and addf-ed or it won't do anything.
Please Log in or Create an account to join the conversation.
- scruffythefirst
- Offline
- New Member
Less
More
- Posts: 17
- Thank you received: 0
02 Aug 2014 22:44 #49441
by scruffythefirst
Replied by scruffythefirst on topic Very basic Pnconf questions - daughter boards
Well the hardware has arrived, and nothing has let the magic smoke out yet!
I bought 2x 7i48's in the end and have both showing up in allhall.txt -
I also got the analogue input working with setting a manual value for the analogue input - custom.hal here, but can't seem to get it to update when Linuxcnc loads
So all I should need to do is change this
#net fro-analogue <= 7i84.analogue.input.name
to
net fro-analogue <= hm2_5i23.0.7i84.0.0.analogin0
I bought 2x 7i48's in the end and have both showing up in allhall.txt -
12 float OUT 0 hm2_5i23.0.7i84.0.0.analogin0
12 float OUT 0 hm2_5i23.0.7i84.0.0.analogin1
12 float OUT 0 hm2_5i23.0.7i84.0.0.analogin2
12 float OUT 0 hm2_5i23.0.7i84.0.0.analogin3
12 float OUT 23.92859 hm2_5i23.0.7i84.0.0.fieldvoltagea
12 float OUT 24.60213 hm2_5i23.0.7i84.0.0.fieldvoltageb
12 bit OUT FALSE hm2_5i23.0.7i84.0.0.input-00
12 bit OUT TRUE hm2_5i23.0.7i84.0.0.input-00-not
12 bit OUT FALSE hm2_5i23.0.7i84.0.0.input-01
12 float OUT 0 hm2_5i23.0.7i84.0.1.analogin0
12 float OUT 0 hm2_5i23.0.7i84.0.1.analogin1
12 float OUT 0 hm2_5i23.0.7i84.0.1.analogin2
12 float OUT 0 hm2_5i23.0.7i84.0.1.analogin3
12 float OUT 23.89314 hm2_5i23.0.7i84.0.1.fieldvoltagea
12 float OUT 24.28308 hm2_5i23.0.7i84.0.1.fieldvoltageb
12 bit OUT FALSE hm2_5i23.0.7i84.0.1.input-00
12 bit OUT TRUE hm2_5i23.0.7i84.0.1.input-00-not
12 bit OUT FALSE hm2_5i23.0.7i84.0.1.input-01
I also got the analogue input working with setting a manual value for the analogue input - custom.hal here, but can't seem to get it to update when Linuxcnc loads
# Include your custom HAL commands here
This file will not be overwritten when you run PNCconf again
# ----analogue input signal conditioning - feed overide------
loadrt conv_float_s32 count=1
addf conv-float-s32.0 servo-thread
loadrt scale count=1
addf scale.0 servo-thread
setp halui.feed-override.count-enable true
setp halui.feed-override.direct-value true
setp halui.feed-override.scale 0.01
#-set gain and offset
setp scale.0.gain 0.585
setp scale.0.offset 0
#-create analogue input signal from 7i84
newsig fro-analogue float
#net fro-analogue <= 7i84.analogue.input.name
#-send analogue signal to scale function
net fro-analogue => scale.0.in
#-convert output from scale to s32
net scale-output <= scale.0.out
net scale-output => conv-float-s32.0.in
net conv-output <= conv-float-s32.0.out
net conv-output => halui.feed-override.counts
So all I should need to do is change this
#net fro-analogue <= 7i84.analogue.input.name
to
net fro-analogue <= hm2_5i23.0.7i84.0.0.analogin0
Please Log in or Create an account to join the conversation.
02 Aug 2014 22:56 #49444
by andypugh
I don't know if that was a question, but if it was the answer is "yes"
I am not sure about your scale gain. You probably want to have a significant number of "counts" in the s32 value, then set the fro-scale to suit. The conversion from float to s32 will convert to integer, so you will lose most of the float data unless you scale it up a bit.
Replied by andypugh on topic Very basic Pnconf questions - daughter boards
#net fro-analogue <= 7i84.analogue.input.name
to
net fro-analogue <= hm2_5i23.0.7i84.0.0.analogin0
I don't know if that was a question, but if it was the answer is "yes"
I am not sure about your scale gain. You probably want to have a significant number of "counts" in the s32 value, then set the fro-scale to suit. The conversion from float to s32 will convert to integer, so you will lose most of the float data unless you scale it up a bit.
Please Log in or Create an account to join the conversation.
- scruffythefirst
- Offline
- New Member
Less
More
- Posts: 17
- Thank you received: 0
25 Feb 2015 05:31 #56281
by scruffythefirst
Replied by scruffythefirst on topic Very basic Pnconf questions - daughter boards
Please Log in or Create an account to join the conversation.
Moderators: cmorley
- Configuring LinuxCNC
- Configuration Tools
- PnCConf Wizard
- Very basic Pnconf questions - daughter boards
Time to create page: 0.196 seconds