7i92/7i77 Yaskawa Servo
- Thank you received: 5302
30 May 2015 07:14 #59219
Replied by PCW on topic 7i92/7i77 Yaskawa Servo
You will have to do both.
Swapping A and B will reverse the encoder direction,
(as will changing the sign of the input scale ini parameter)
but now you will have positive feedback and a instant runaway
so the analog output must be reversed also
This is done in the hal file by changing the sign of the scalemax
parameter for the axis you wish to change
For example instead of
setp hm2_5i25.0.7i77.0.1.analogout0-scalemax 10
you would have
setp hm2_5i25.0.7i77.0.1.analogout0-scalemax -10
you would have
30 May 2015 07:17 #59220
Edit: just noted you have P value of -10? P values should be positive
you would have
you would have
30 May 2015 07:36 #59221
you would have
you would have
- pmcstoneinc
30 May 2015 08:41 #59223
by pmcstoneinc
Replied by pmcstoneinc on topic 7i92/7i77 Yaskawa Servo
OK that worked perfectly reversing the outputs. Still getting following erros. I think I will have to double check settings in the INI. Thanks for all the help Peter!
Dan
Dan
- pmcstoneinc
31 May 2015 03:15 #59242
by pmcstoneinc
Peter will I have to re-tune the servo amp PID settings? I have the axis stable and holding position, Encoder scale is correct. But when I try to do a incremental move of 1mm the axis is moving 25.xx mm then proceeding with a following error. Let me know your thoughts. Thanks.
31 May 2015 03:30 - 31 May 2015 03:32 #59243
Sure sounds like feedback is backwards so you get an instant runaway when you try to jog
edit: what are your P,I,D, FF1 settings?
Last edit: 31 May 2015 03:32 by PCW.
- pmcstoneinc
31 May 2015 03:32 #59244
by pmcstoneinc
I inverted the output pin and physically switched the A and B channels, with no luck......
31 May 2015 03:39 - 31 May 2015 03:40 #59246
Well if you do both, if the feedback was backwards it will still be backwards
Its better to do things systematically
1. Get encoder inputs scaled properly and in the proper direction (and never change again)
2. Verify you have negative feedback (positive feedback= runaway)
You can do this by setting the PID values to 0 and FF1 to say 1 and then doing a jog
if the jog moves in the correct _direction_ as determined by the _change_ in the DRO
(the distance will be wrong) the feedback is correct. If the feedback is incorrect,
change the analog output polarity
Last edit: 31 May 2015 03:40 by PCW.
- pmcstoneinc
31 May 2015 03:51 - 31 May 2015 03:52 #59247
by pmcstoneinc
Yes the encoder is scaled and in the proper direction. Sorry I did not clarify that I did each process individually and not both at the same time. Ha!
The axis moves as commanded manually and in the right direction, but why do I get a following error? Is there an issue with my output_scale and output_min/max values?
Last edit: 31 May 2015 03:52 by pmcstoneinc.
31 May 2015 03:59 #59248
can you post your hal and ini files?
A 25 mm error means something basic is wrong (runaway or no control)
Time to create page: 0.222 seconds