[ Vfdmod ] An easy VFD control over MODBUS RTU
as most use the system internal mb2hal comp and now this jups in on a deb install only view are using
Please Log in to join the conversation.
aekhv wrote: It seems communication settings wrong (error code 110), check parameters in RS485 group. And please show your ini file here.
i have same error i cant solve it...
I have VFD-E delta
i adjust the setting in the VFD for baudrate but still i m getting error 110... in my windows it work with Delta VFDsoft
there is ASCII and RTU
also RTU modbus,
and ASCII modbus,
which protocol should work with this
Attachment not found
Please Log in to join the conversation.
Vfdmod works in RTU mode, ASCII mode is not supported. According to your INI file I see communication speed is 9600 baud, 8N1. Be sure your VFD is configured on the same way: parameter 9.08 should be 1, and 9.09 should be 6. Also check VFD slave address, it should be set to 1 as it specified in your INI file.
Please Log in to join the conversation.
aekhv wrote: Hi taloot,
Vfdmod works in RTU mode, ASCII mode is not supported. According to your INI file I see communication speed is 9600 baud, 8N1. Be sure your VFD is configured on the same way: parameter 9.08 should be 1, and 9.09 should be 6. Also check VFD slave address, it should be set to 1 as it specified in your INI file.
yeah i did same but no luck,,, i used the VFDB component and it works well i used ur generator to make the pyvcp and it work fine (after manually edit it ) ,,
i just need to add some monitoring parameter to source driver,, do u have any idea how can i compile the vfd , component submake file
Please Log in to join the conversation.
Also it would be nice if you attach some debug output (loadusr -W vfdmod --debug ...), maybe it will help to fix your problem
Please Log in to join the conversation.
I'm trying to get my Fuling VFD from terminal control to Modbus with no luck. I've checked the 9600 n, 8, 1 settings on the VFD twice.
Any thoughts on this debug?
Attachment not found
Please Log in to join the conversation.
Please Log in to join the conversation.
Thanks for your quick reply last night and happy new year from Australia.
Increasing the ProtocolDelay to 7 fixed the com problem.
But now cant get the VFD to turn the spindle. Forward and Rev lights work on the VFD.
Looks like the Fuling needs special commands?
forum.pv-automation.com/viewtopic.php?p=52#p52
Any thoughts?
srl
Please Log in to join the conversation.
As I see from debug output the control register address is 0x1000, and vfdmod sends 0x0005 to it. What values do you use to turn spindle on and off? According to table at your link it should be 0x0001 (run forward) and 0x0005 (stop).
Could you show your ini file please?
Please Log in to join the conversation.
I used the file vdf-dzb280.ini posted earlier in this thread, the control values are wrong.
The changed file attached.
All fine now.
No reverse but thats ok, setting foward run and fwd light up on the VFD. Reverse its stop and rev.
Attachment not found
Thanks again.
srl