can 7i76 have"is_opendrain" for enable ?
22 Apr 2016 14:33 #73717
by Alicee
can 7i76 have"is_opendrain" for enable ? was created by Alicee
I am trying to understand HAL configuration. Can you please help about this:
For example I am looking at these line in my HAL file:
net y-enable hm2_5i25.0.7i76.0.0.output-03
net y-enable <= axis.1.amp-enable-out
net y-enable => hm2_5i25.0.stepgen.01.enable
I think I can see that axis.1.amp-enable-out is connect to to net y-enable and that also connect to hm2_5i25.0.stepgen.01.enable and also connect same (of those 3way net) to hm2_5i25.0.7i76.0.0.output-03.
My question is there way to make hm2_5i25.0.7i76.0.0.output-03 into open collector/drain type?
I saw "is_opendrain" in HOSTMOT manual, but it looks like only for full GPIO pin.
And if that will works for 7i76 pin that I will use to enable external driver amp then what is syntax?
would it look like: hm2_5i25.0.7i76.0.0.output-03-is-opendrain or something else or not possible?
And if that will work then when y-enable == true then 7i76 03 is HiZ and when y-enable == false 7i76 03 is GND ?
or
If "is_opendrain" is not possible then when y-enable == true then 7i76 03 is +VField and when y-enable == false 7i76 03 is GND ?
Thanks!
For example I am looking at these line in my HAL file:
net y-enable hm2_5i25.0.7i76.0.0.output-03
net y-enable <= axis.1.amp-enable-out
net y-enable => hm2_5i25.0.stepgen.01.enable
I think I can see that axis.1.amp-enable-out is connect to to net y-enable and that also connect to hm2_5i25.0.stepgen.01.enable and also connect same (of those 3way net) to hm2_5i25.0.7i76.0.0.output-03.
My question is there way to make hm2_5i25.0.7i76.0.0.output-03 into open collector/drain type?
I saw "is_opendrain" in HOSTMOT manual, but it looks like only for full GPIO pin.
And if that will works for 7i76 pin that I will use to enable external driver amp then what is syntax?
would it look like: hm2_5i25.0.7i76.0.0.output-03-is-opendrain or something else or not possible?
And if that will work then when y-enable == true then 7i76 03 is HiZ and when y-enable == false 7i76 03 is GND ?
or
If "is_opendrain" is not possible then when y-enable == true then 7i76 03 is +VField and when y-enable == false 7i76 03 is GND ?
Thanks!
Please Log in or Create an account to join the conversation.
22 Apr 2016 14:40 #73718
by PCW
Replied by PCW on topic can 7i76 have"is_opendrain" for enable ?
No, the field outputs on the 7I76 are sourcing only
(They supply the field voltage when on and are open when off)
(They supply the field voltage when on and are open when off)