Locking indexer issues
  • COlger81
  • COlger81's Avatar Topic Author
  • Elite Member
  • Elite Member
08 Oct 2020 14:12 #185382 by COlger81
Locking indexer issues was created by COlger81
Are there any known issues with the "locking indexer" function? While rotary is locked with air brake, and servo is on hold (no command input to servo), encoder walks out of position until estop is caused by following errors. The servo shaft is not turning and rotary is not moving so this is a tough one to solve.
08 Oct 2020 15:43 #185394 by Todd Zuercher
Replied by Todd Zuercher on topic Locking indexer issues
So you are saying that even though everything is mechanically locked your encoder is counting up or down?
If that is the case you need to check for an electrical problem in your encoder system. Either it is picking up electrical interference causing false counts, or there is a short or bad connection somewhere causing false counts.
Check your grounds, are you using shielded cables, are the shields properly grounded (at only one end).
  • COlger81
  • Elite Member
  • Elite Member
09 Oct 2020 08:51 #185461 by COlger81
Replied by COlger81 on topic Locking indexer issues
Yes, mechanically locked and encoder freaks out as soon as a milling load is applied to part. When tool contacts part, it initially might fluctuate 1 or 2 encoder counts, then over a few seconds, with no mechanical movement. Encoder counts freak out and following errors trip estop.
Yes, shielded CAT6 cable with proper shielding on one end. I'm suspecting a faulty drive if there's no known bugs with locking indexer function.
Is there a way to ignore position of A axis while brake is locked? It would at least help me with diagnosing.
09 Oct 2020 09:28 #185470 by Todd Zuercher
Have you tried plotting the encoder A and B signals with Halscope when the problem is occurring and when it isn't for comparison. Also, looking at those signals with a real scope might be enlightening.
  • COlger81
  • Elite Member
  • Elite Member
09 Oct 2020 09:37 #185472 by COlger81
It's showing over and under shoot but nothing is mechanically moving. This is a DMM DYN4 which simulates encoder counts to feed 7i77. It does not actually directly pass through raw encoder signals.
09 Oct 2020 09:43 #185474 by Todd Zuercher
All bets might be off then. Is the drive being disabled when in "locked" mode?
You might need to contact DMM and ask their opinion what might be going on with their goofy encoder.
  • COlger81
  • Elite Member
  • Elite Member
09 Oct 2020 10:02 #185480 by COlger81
Yes, drive is "disabled". DMM has a "SHOLD" input that is verified functioning. They call it a servo hold which is goofy. Faulty encoder or drive most likely.
09 Oct 2020 11:12 #185487 by Mike_Eitel
Replied by Mike_Eitel on topic Locking indexer issues
You sometimes can improve the shilding against high frequencies when you connect the free shield end via a low inductive capacitor. Fx. a ceramic one.
Mike
Time to create page: 0.497 seconds