CINCINATTI MILACRON ARROW 500 (BDS4 + VFS5) WITH MESA 7i77 + 6i25 WITH LINUXCNC
1 year 7 months ago #324278 by UrKibin
Hi all,
I tried one axis first to be safe.
If encoders are disabled in HAL file, I can move the y-axis freely. no shaking. everything is smooth.
But if encoders are enabled, I have varying results.
a lower scale (819.2) - joint 1 following error
a higher scale (4096) - no error but shaking occurs
May PID settings are
P - 50
I - 0
D - 0
Ballscrews are around 10mm
Regards,
Kibin
1 year 7 months ago - 1 year 7 months ago #324295 by PCW
I would use the higher resolution, perhaps increase the following error limits
and proceed to tuning.
If you have oscillation, reduce your P term.
For velocity mode drives, most of the tuning is setting the correct FF1 term
If you set the analog scaling to machine units per second at 10V, FF1=1.00
You can change the PID values live with the "Calibrate"  window.
Last edit: 1 year 7 months ago by PCW.
The following user(s) said Thank You: UrKibin
1 year 7 months ago #324335 by UrKibin
Hi PCW,
Noted on this. Ill first wire the enable of mesa 7i77 to the enable of the servo drive bds4 since I found out that there is a difference in bias/balance (adjustment for zero movement upon drive enablement) if I force enable (jumping the enable of the servo drive (Daredevil)) instead of the mesa board.
I'll first connect the ENAn of the 7i77 to the servo drives so that once the drives are enabled, there will be no movement.
After that, will follow your instructions and use 4096 as a scale starting point to fine tune one axis.
Thank you for your advise.
Regards,
Kelvin
1 year 7 months ago #324404 by UrKibin
Hi All,
Good day. Managed to wire the ENA to the servo drive enable.
My current problem is overshoot. It is overshooting. lets say I command it y5, it will go until y6 then go back to y5. Overshoot increases as feed speed increases. I estimate it to be 1mm per 100mmpm. so 100mmpm has an overshoot of 1mm, 300mmpm has an overshoot of 3mm.
PID settings are
P = 1.5 (If i add more, it shakes at higher speed)
I = 0
D = 0 (any increase and the system shakes)
Scale : 1225 (0.01 accuracy even with overshoots)
1 year 7 months ago - 1 year 7 months ago #324405 by UrKibin
Hi All,
My current problem is overshoot. lets say I command it y5, it will go until y6 then go back to y5. Overshoot increases as feed speed increases. I estimate it to be 1mm per 100mmpm. so 100mmpm has an overshoot of 1mm, 300mmpm has an overshoot of 3mm.
PID settings are
I = 0
FF0 = 0
FF1 = 1
FF2 = 0
Regards,
Kibin
Last edit: 1 year 7 months ago by UrKibin.
Time to create page: 0.278 seconds