08 Apr 2025 15:02 #325939 by unknown
One thing you need to remember is that the PSU have an initial inrush current that is greater than the max current the PSU draws when running.
I went with fuses rather than circuit breakers.
The following user(s) said Thank You: behai

Please Log in or Create an account to join the conversation.

More
08 Apr 2025 15:49 #325941 by behai

One thing you need to remember is that the PSU have an initial inrush current that is greater than the max current the PSU draws when running.
I went with fuses rather than circuit breakers.
 

Thank you Rob. I have found the following specs on the MDR-100-24 PSU:



The full PDF document address is: 100W Single Output Industrial DIN Rail Power Supply MDR-100 series
Best regards,

...behai.

Please Log in or Create an account to join the conversation.

  • tommylight
  • tommylight's Avatar
  • Away
  • Moderator
  • Moderator
More
08 Apr 2025 16:11 #325943 by tommylight
We use these:

It's a fuse and a switch in the same box, the picture shows 2 of them.
Attachments:
The following user(s) said Thank You: behai

Please Log in or Create an account to join the conversation.

More
08 Apr 2025 19:14 #325953 by rodw
For a control box, the simplest way is to use a switched, EMI filtered and fused IEC connector
www.amazon.com.au/uxcell%C2%AE-IEC320-Sw...Filter/dp/B01FT0VRTS
You can see one of these used at the bottom right of my photo shared earlier.

But in your case, this won't work if you want to switch the router on and off because the current of the router will be too high for the typically 6 amp AC rating. Plus you would not want the electrically noisy router to be on the same side of the EMI filter as your electronics.

So in your case, I would use a fixed power lead and a cable gland to bring mains into the control box to two household breakers around 10 amp. One of these will protect your router circuit and the other your electronics, On the electronics circuit, immediately after the breaker, fit an EMI filter
www.jaycar.com.au/240v-ac-emi-filter/p/MS4001
Then connect all of your power supplies to the filtered mains power.

Filtering the power is really important to avoid spurious triggering from electrical noise. I learnt the hard way.

The next thing to work out is your estop. That's a bit tricky because you need to disable the router and the stepper motor power supply without using any relays that could fail. The estop needs to drop power to your router power and  stepper mains motion. You could use 2 phases of a 3 phase breaker but technically you would then need  to use a safety relay to be compliant.
Its probably acceptable to disable your stepper drivers using the enable pins on them that are usually left disconnected.

 
The following user(s) said Thank You: behai

Please Log in or Create an account to join the conversation.

More
09 Apr 2025 07:43 #325967 by behai

For a control box, the simplest way is to use a switched, EMI filtered and fused IEC connector
www.amazon.com.au/uxcell%C2%AE-IEC320-Sw...Filter/dp/B01FT0VRTS
You can see one of these used at the bottom right of my photo shared earlier.

But in your case, this won't work if you want to switch the router on and off because the current of the router will be too high for the typically 6 amp AC rating. Plus you would not want the electrically noisy router to be on the same side of the EMI filter as your electronics.

So in your case, I would use a fixed power lead and a cable gland to bring mains into the control box to two household breakers around 10 amp. One of these will protect your router circuit and the other your electronics, On the electronics circuit, immediately after the breaker, fit an EMI filter
www.jaycar.com.au/240v-ac-emi-filter/p/MS4001
Then connect all of your power supplies to the filtered mains power.

Filtering the power is really important to avoid spurious triggering from electrical noise. I learnt the hard way.

The next thing to work out is your estop. That's a bit tricky because you need to disable the router and the stepper motor power supply without using any relays that could fail. The estop needs to drop power to your router power and  stepper mains motion. You could use 2 phases of a 3 phase breaker but technically you would then need  to use a safety relay to be compliant.
Its probably acceptable to disable your stepper drivers using the enable pins on them that are usually left disconnected.


 

Thank you Rod,

I have been thinking about your advice on the router, I am trying something I don't have any practical knowledge of, I will just leave this one out, I will get the other three working, as my knowledge increase, I might rewire it again. This just my hobby project. But I really like learning electronics now, I have always been afraid of it.

You are right, the ENABLE pin on the CLT57T-V41 is left unconnected. During my learning of this driver, I used only the Raspberry Pi 4 and Python to program it, setting ENABLE to high disables the motor.

Best regards,

...behai.
 
The following user(s) said Thank You: rodw

Please Log in or Create an account to join the conversation.

More
09 Apr 2025 07:51 #325970 by behai

...
It's a fuse and a switch in the same box, the picture shows 2 of them.
 


Thank you tommylight,

I understand now. When I searched for "automatic fuses", I did get correct result, such as this one www.aurinkopaneelikauppa.fi/Automatic-Fu...30V-AC-slow-Type-C-2; but I confused them for circuit breakers.

Best regards,

...behai.

 
The following user(s) said Thank You: tommylight