Modbus communication error

More
20 Jan 2020 11:37 #155247 by cmorley
Replied by cmorley on topic Modbus communication error
Sorry I meant set offset to 1

Please Log in or Create an account to join the conversation.

More
20 Jan 2020 11:39 - 20 Jan 2020 11:42 #155248 by jsskangas
Replied by jsskangas on topic Modbus communication error
Hello

2100 and 2101 are correct. i tried them both, in hex value and in decimal.
I also tried different offsets 0-9. none made difference.




Attachments:
Last edit: 20 Jan 2020 11:42 by jsskangas.

Please Log in or Create an account to join the conversation.

More
20 Jan 2020 12:16 - 20 Jan 2020 12:17 #155249 by cmorley
Replied by cmorley on topic Modbus communication error
Its about 4am here so i'm getting hazzy...

When I said element offset I meant the radio button in classiclader's modbus configuration page - it's either 0 or 1

anyways the command send seems ok but is different from your program - if I'm reading it right:

your program 0103210000018e36 broken up is 01 03 2100 0001 8e36
meaning slave 1, function 3, address 2100H, number of bytes 1, then checksome

from classicladder:
INFO CLASSICLADDER-   Modbus I/O module to send: Lgt=8 <-  Slave address-1  Function code-3  Data-8 34 0 1 C7 A4 
meaning slave 1, function 3, address 0834H, number of bytes 1, then checksome

oh wait - in classic ladder the '1st modbus element' must be input as a decimal 8448 - not 2100

In my test config then the message is the same as your program:
INFO CLASSICLADDER-   Modbus I/O module to send: Lgt=8 <-  Slave address-1  Function code-3  Data-21 0 0 1 8E 36
That looks better...
Last edit: 20 Jan 2020 12:17 by cmorley.

Please Log in or Create an account to join the conversation.

More
20 Jan 2020 13:33 #155254 by jsskangas
Replied by jsskangas on topic Modbus communication error
Solved.
Thanks.

It was HEX address in VFD and one should input address in linuxnc as DEC.

now works.
The following user(s) said Thank You: Clive S

Please Log in or Create an account to join the conversation.

More
20 Jan 2020 20:35 #155272 by cmorley
Replied by cmorley on topic Modbus communication error
Thats great!
Could you post the terminal print out of classicladder so I can see the correct returned result from the VDF - I an adding some docs to linuxcnc to help next time.
Thanks

Please Log in or Create an account to join the conversation.

More
20 Jan 2020 20:57 #155273 by jsskangas
Replied by jsskangas on topic Modbus communication error
I will tomorrow.
Just went to sleeping...

Please Log in or Create an account to join the conversation.

More
21 Jan 2020 11:37 #155310 by jsskangas
Replied by jsskangas on topic Modbus communication error
Hello

Here is some debug dump.


INFO CLASSICLADDER- Modbus I/O module received: Lgt=15 -> (Slave address-1 - Function code-3 ) A 0 0 5 0 0 0 0 0 0 0 E4 89
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 0 0 1 43 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 0 0 1 43 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 1 0 0 D3 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 1 0 0 D3 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-21 0 0 5 8F F5
INFO CLASSICLADDER- MODBUS Length we should receive=12 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
15 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=15 -> (Slave address-1 - Function code-3 ) A 0 0 5 0 0 0 0 0 0 0 E4 89
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 0 0 1 43 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 0 0 1 43 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 1 0 0 D3 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 1 0 0 D3 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-21 0 0 5 8F F5
INFO CLASSICLADDER- MODBUS Length we should receive=12 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
15 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=15 -> (Slave address-1 - Function code-3 ) A 0 0 5 0 0 0 0 0 0 0 E4 89
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 0 0 1 43 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 0 0 1 43 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 1 0 0 D3 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 1 0 0 D3 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-21 0 0 5 8F F5
INFO CLASSICLADDER- MODBUS Length we should receive=12 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
15 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=15 -> (Slave address-1 - Function code-3 ) A 0 0 5 0 0 0 0 0 0 0 E4 89
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 0 0 1 43 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 0 0 1 43 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 1 0 0 D3 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 1 0 0 D3 CA
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-21 0 0 5 8F F5
INFO CLASSICLADDER- MODBUS Length we should receive=12 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
15 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=15 -> (Slave address-1 - Function code-3 ) A 0 0 5 0 0 0 0 0 0 0 E4 89
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-6 Data-20 0 0 1 43 CA
INFO CLASSICLADDER- MODBUS Length we should receive=5 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
8 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=8 -> (Slave address-1 - Function code-6 ) 20 0 0 1 43 CA

Please Log in or Create an account to join the conversation.

More
21 Jan 2020 11:52 #155312 by cmorley
Replied by cmorley on topic Modbus communication error
Thank you!