REQUEST TB4 PINOUT VERIFICATION FOR 7I76 VFD NFLIXIN 9600image missing https://www.RC-o2.com/RCo2/PUBLIC/Screenshot_2023-02-04_12-14-38.png
7I76 TB4
1 SPINDLE- ==> ACOM
2 SPINDLE OUT ==> A1
3 SPINDLE+ ==> AM
5 SPINDLE ENA- ==> ACOM
6 SPINDLE ENA+ ==> X5 FWD
7 SPINDLE DIR- ==> X6 REV
A1 = ANALOG INPUT 10V
AM = ANALOG OUTPUT 10V
MANUAL:
nflixin.com/en/?p=217
THE VFD 9600 POWERS ON ALTHOUGH NO RESPONSE FROM SIGNALS SENT FROM 7I76 TO THE 9600 TERMINALS.
PO-00 G/P TYPE DISPLAY
1: G TYPE CONSTANT TORQUE
2: P TYPE VARIABLE LOAD
P0-01 MOTOR 1 CONTROL MODE
0 SPEED SENSORLESS VECTOR CONTROL SVC
3 VF CONTROL
P0-02 COMMAND SOURCE SELECTION (INPUT FROM BUTTONS OR DATA)
0 = PANEL BUTTONS
2 = TERMINAL CONTROL
3 = COMMUNICATION CONTROL
P0-27 BINDING COMMAND SOURCE TO FREQUENCY SOURCE
2 = A1
P5-07 AM FUNCTION SELECTION
5 = OUTPUT VOLTAGE
P4-34 SET A2 INPUT SIGNAL SELECTION
0 = VOLTAGE
1 = CURRENT SIGNAL
P0-03 MAIN FREQUENCY SOURCE (INPUT FOR SPINDLE FREQUENCY)
2 = A / 1
P8-18 STARTUP PROTECTION
0 = NO
1 = YES
P9-00 MOTOR OVERLOAD PROTECTION
0 = NO
1 = YES
P9-12 INPUT PHASE LOSS PROTECTION / CONTACTOR ENERGIZING PROTECTION SELECTION
0 = DISABLED
1 = ENABLED
P8-27 TERMINAL JOG PREFERED
0 = DISABLED
1 = ENABLED
P8-45 A1 INPUT VOLTAGE LIMIT LOWER
3.1V
ATTRIBUTE TO 0?
P8-46 A1 INPUT VOLTAGE LIMIT UPPER
P8-45 TO 3.10V
ATTRIBUTE TO 10V?
P9-47 FAULT PROTECTION #1
0 = MOTOR COAST TO STOP
P9-59 ACTION INSTANT POWER FAILURE
2 = DECELERATE TO STOP
A7-01 SELECT CONTROL MODE OF OUTPUT TERMINALS ON CONTROL BOARD
0 = CONTROL BY AC DRIVE
TEN THOUSANDS DIGIT = AM