( Solved ) Mesa 7i76 encoder problem
28 Jul 2020 08:13 #176242 by Clive S
Replied by Clive S on topic ( Solved ) Mesa 7i76 encoder problem
It could also be a 5I25 or cable problem
I have re seated the 5i25 and the cable. Would re flashing the card help. or is there anyway to test.
I do have the 7i76e could the 7i76 be plugged into that to test with the correct firmware.
I also have a 7i96
28 Jul 2020 09:03 #176246 by PCW
Replied by PCW on topic ( Solved ) Mesa 7i76 encoder problem
If the card was working, reflashing will not help.
Reflashing basically never helps unless you need to change
the firmware or replace corrupted firmware, but corrupted
firmware on a 5i25 will result in loading the fallback config
which has no encoders or stepgens so will be obvious.
Can you read the input-a pin state when the
7I76 is not connected vs connected (with encoder unplugged)?
That will verify if the 5I25 is OK
It should read high if the 7I76 is unconnected and
low if the 7I76 is connected if the 7I76 is jumpered for
TTL mode and the encoder is unplugged
To load the driver and read pins without the 7I76 you can do this:
halrun
halcmd: loadrt hostmot2
halcmd: loadrt hm2_pci config=" "
halcmd: loadrt threads name1=servo-thead
halcmd: start
halcmd: addf hm2_5i25.0.read servo-thread
halcmd: getp hm2_5i25.0.encoder.00.input-a
The following user(s) said Thank You: Clive S, zfa
29 Jul 2020 06:06 - 29 Jul 2020 07:57 #176350 by Clive S
halrun
halcmd: start
Ok With the encoder unplugged from the 7i76
7I76 is unconnected
A shows true
B shows true
Rebooted then:-
7I76 is connected
A shows true
B shows true
Does this mean the 5i25 is faulty. I have not changed the PP cable but is is a good quality one and short
Last edit: 29 Jul 2020 07:57 by Clive S.
29 Jul 2020 08:41 #176388 by PCW
I would guess that the 5I25 is OK but both A and B should be low
when the 7I76 is connected (and the encoder is unconnected)
Are you sure the 7I76 is jumpered for TTL mode?
29 Jul 2020 09:45 #176391 by Clive S
I don't understand it this has be running for a few years. I have just checked and you are of course correct, they were wrong.
They are now set as single ended now it is working again.
Could it have worked before ? !!
Many thanks for the patience.
  • Moderator
  • Moderator
29 Jul 2020 10:01 #176393 by tommylight
Replied by tommylight on topic ( Solved ) Mesa 7i76 encoder problem
Set the title as solved as it was not sticking .
29 Jul 2020 12:13 #176401 by PCW
It can sort-of work with single ended signals and differential inputs
because you can develop a 100 mv or so differential input with single
ended signal because of the way the termination works.
29 Jul 2020 12:18 #176402 by Clive S
Thanks that explains a lot.
It must have been just on cusp of it working.
Moderators: PCW, jmelson
Time to create page: 0.735 seconds