7i76e SPINDLE OUT voltage is slightly low
5 years 10 months ago #193597 by jpvonoy
I think PCW is right that it is likely a noise/EMI issue. I have this connected with unshielded cable for testing. The shielded cable arrives tomorrow, so I'll see if that helps, then I'll look for other sources of EMI.
chris@cnc wrote: Try Parameter PD71 or PD159 to adjust target speed. Any VDF should compensate this kind of Problem only Parameter are Different. Or increase P of your VFD. Something must be happened.
Thanks for those suggestions. I tried adjusting PD71 through the full range and it had no effect on the spindle speed. I may try PD159 after going down the EMI route.
Mike_Eitel wrote: What kind of motor do you use?
Are you aware of motor slip.
The frequency of vfd is equal to physical only when it's a synchron motor.
Mike
This is a 3 phase 400Hz motor: www.amazon.com/Huanyang-Spindle-Milling-...aving/dp/B07LG233LM/
I was not aware of motor slip. I will read up on that, thanks.
5 years 10 months ago #193743 by Muzzer
Bear in mind that if your spindle is 3-4% out on speed it really won't make the slightest difference to anything. It might be slightly irritating but the tool doesn't care about that.
Some VFDs can compensate for slip based on the load current which is itself largely proportional to load. If you have told it that the base speed is 1425rpm with a line frequency of 50Hz, it knows that the slip frequency at rated load is 50 - 47.5Hz ie 2.5Hz, so it can increase the output to 52.5Hz, proportional to load. Don't know if Huanyang supports that feature.
Simplest fix might be to set max frequency to 3-4% above nominal in the Huanyang setup.
5 years 9 months ago #193792 by jpvonoy
Muzzer wrote: Bear in mind that if your spindle is 3-4% out on speed it really won't make the slightest difference to anything. It might be slightly irritating but the tool doesn't care about that.
Understood. I'm more interested in understanding the workings of my system. If there was something wrong, I wanted to find out what it was and fix it.
Muzzer wrote: Some VFDs can compensate for slip based on the load current which is itself largely proportional to load. If you have told it that the base speed is 1425rpm with a line frequency of 50Hz, it knows that the slip frequency at rated load is 50 - 47.5Hz ie 2.5Hz, so it can increase the output to 52.5Hz, proportional to load. Don't know if Huanyang supports that feature.
I haven't seen anything for slip compensation in the parameter settings. The max frequency of the drive is 400 Hz and I already have it set there, so I can't increase frequency further.
With the replies so far, I'm satisfied that there isn't an easy fix that I'm missing. So, I'll leave it the way it is right now.
Oh, and I also replaced the spindle control wiring from 7I76E TB4 to the VFD with shielded cable and it didn't change anything. As part of some other upgrades I'm doing, I will be replacing more wiring with shielded cable and switching to a different electronics box, so I'll revisit this once all the changes are complete.
5 years 9 months ago #194114 by jpvonoy
Just an update on what I've been doing related to this. I switched from the analog spindle speed control to RS-485 control, just for the sake of learning.
With RS-485 control, the actual spindle speed is much closer to commanded. Less than 1% across the operational range, with most values less than 0.5% off.
As long as it doesn't cause latency issues on the Raspberry Pi 4 I'm using, I'll use this method for control going forward. It saves installing about 10 wires and a few disconnects on my electronics box, as well as a much simpler setup.
Moderators: PCW, jmelson
Time to create page: 0.327 seconds