Mesa 7i96s pktUAT on P1
27 Sep 2024 21:13 #310919 by PCW
Replied by PCW on topic Mesa 7i96s pktUAT on P1
Because the 7I96S RS-485 interface is 6 pins of TB2 (15 .. 20)
and has a 6 pin connector.
28 Sep 2024 16:29 #310988 by nartburg
Replied by nartburg on topic Mesa 7i96s pktUAT on P1
The answer is:
0000EBFF
00002BFF
00006BFF
and it dosent care if the loopback is connected or not
the 6 pin plug is this the contraption with resistors?
28 Sep 2024 19:07 #310993 by PCW
If that result is with RX+ connected to TX+ and RX- connected to TX-
on the plug, and this is a 7I96S, then the RS-485 interface has been damaged.
29 Sep 2024 14:55 #311029 by nartburg
Hi PCW,
thx for your effort.
OK-- I just realise your strategy : We tested P1 and found the Hardware OK at P1 and than I fell into a trap with the loopback ---I assumed we were going to something similar to what you have been suggesting in
forum.linuxcnc.org/38-general-linuxcnc-q...-modbus-help?start=0
loop the onboard rs-485 to the pktUARTS on P1 so yesterdays results were the results of such a test.
But you wanted me to test a direct loopback from RX+ to TX+ and RX- to TX- of the onboard RS-485 -- sry my fault
The result of this test is:
without loopback:
0000EBFF
00002BFF
00006BFF
with loopback:
0000EBFF
00000BFF
00006BFF
29 Sep 2024 18:52 #311039 by PCW
That indicates that the RS-485 interface is OK
30 Sep 2024 07:23 #311056 by nartburg
Perfect!
We established that P1 is Working and the on board rs-485 is working.
Now we can move on to the start:
How to implement pktUART on P1?
30 Sep 2024 15:28 #311071 by PCW
I think your bit file should work (assuming your external RS-485 interface
automates RS-485 driver enable control)
The fact that you could not get the RS-485 interface on TB2 to operate
suggests a test issue.