3 years 9 months ago #262583 by new2linux
sivaraj, many, many thanks! The 401 alarm (VRDY OFF) is the current alarm. There is no 100 volt AC at Terminal strip T1, Terminals 5 and 6. Yes, the ladder diagram, parameters & diagnoses will appear on-screen.
What you say about the 900 series parameters need to be loaded 1st & P38 requirements; sounds correct, I was not asked (nice to know this) to do this 1st then the RS232 will work. Is it your opinion to start from a fresh blank memory and reload the .OMC & .DNC files for the parameters and diagnostics data? So I need to un-power the battery backup and allow the machine to set for 20 seconds?
P38 is this the line? N0038 P 00001000
These are the lines that were difficult. The line 304 needs to be 00000011; 309 needs to be 00000001; 314 needs to be 00000000, if you key in the correct value it will not accept or
save.
The last suggestion was to check all the limit switches to see if any are stuck because it appears to be e-stop related, I plan to review this unless you suggest to clear memory and I try the parameters and diagnostics data again.This is the 900 code I have, there are all 0s after line 921. (I was looking for a better way to post this)
N0900 P 00111001
N0901 P 01000100
N0902 P 00100000
N0903 P 10010000
N0904 P 00000000
N0905 P 00101000
N0906 P 00000000
N0907 P 01010100
N0908 P 00000000
N0909 P 01000011
N0910 P 00010010
N0911 P 00000100
N0912 P 00000000
N0913 P 10000000
N0914 P 00000000
N0915 P 00100000
N0916 P 00000100
N0917 P 00000010
N0918 P 00000000
N0919 P 00000000
N0920 P 00000000
N0921 P 00000001
Many thanks!
3 years 9 months ago #262660 by new2linux
andypugh, thank you for your help. The spindle has a belt driven "Positioncoder" with this information on the label: A860-0309-T302; No. ZA-0251669 120605; N1018523. This "coder" cable, plugs in the bottom of the spindle servo amplifier, the cable (a real set of wires) to the optical device plugs in to the same spindle servo amplifier, at a different location.
I have not had access to the x, y or z servo encoder, it looks like the z or x axis (are the easier motor to access) motor will need to be removed to get to see the encoder, I will do that if the above information is not acceptable.
The best I could hope for would be if the spindle motor could be disconnected after finishing the "baseplate" with hope is to mount a hi-speed single phase spindle to the end of the BT-40 machine spindle, even if it required a (properly sized) static-phase converter (vs. the 10HP RPC).
Many thanks, all suggestions are warmly welcomed.
3 years 9 months ago - 3 years 9 months ago #262681 by new2linux
sivaraj, thanks! Over the weekend, I have used the Reset & Delete while pressing Power On button to delete and start new. Now, I have the flashing LSK then using a verified correct cable (the other cable was straight through) but was unable to transfer data.
I keyed in the 900s and the P38 as; N0038 P 00001000 as stated. Is this the correct approach? The LSK needs a certain way (the "real key=1" & in MDI not Edit & PWE=1) to start, but at the end when PC sending says all sent the LSK will continue to flash, no way back to PWE to make = 0, so never saves, or never arrived, so use Off/On, on panel.
I have new rs232 ends to make new cable ordered, the current is molded end and I cut off old used end & used a solder on, "tests ok" with ohm meter to the proper "pin out" this weekend. There are a few limit switches that I have not checked.
Wondering your thoughts or suggestions?
Many thanks!
Last edit: 3 years 9 months ago by new2linux.
3 years 9 months ago - 3 years 9 months ago #262700 by sivaraj
save.
Sorry for delay in reply due to week end
I suspect Emergency Circuit problem ,
Either Emergency limit switch struck or the wire broke .
Please trace the input wiring of X021.4 in Electrical circuit and PLC logic for G121.4 in ladder.
Usually G121.4 will have ladder logic which will power On the supply to drives
I assume inputs values on D300/D305/D310/D315 are timer values.
Only D300/D305/D310/D315 values you can set.
The Next 4 values of timers datas are controlled by the PLC ladder program .
You may not be able to write these values.Just ignore it
The Parameter N0038 P 00001000 says you have a Full Keyboard.
Can you please check where the RS232 port cable is connected in CNC Connector (M5 or M74)
Accordingly we need to set the device and communication parameter.
Fanuc default protocol is 4800, E, 7, 2 ( Parameter 552/553=10)
To upload/download parameters from PC using data Punch IN or OUT
1) CNC should be in EDIT mode
2) PWE=1 and
3)Edit key should be in ON only for diagnosis data input.
If Edit mode is not possible, the only option is to enter the parameters by manual input in MDI mode.
I have enclosed pages from Fanuc Manual for your reference
As you have cleared the parameter now I will request enter the parameter list manually.
After fixing the Emergency Stop circuit issue you may chase the RS 232 I/O issue.
1).First enter 900 series parameters (900~921) and P38.
2). Power Off and On
3).Enter the parameters 0~900
4).Enter Servo parameter
you can do this in DGNOS/PARAM button >SV-PRM soft key
or
in parameter 8n00 & 8n20~8n24
Set values of 8n20~8n24 and 8n00=00 (Initial setting of digital servo parameter is done)
n=1,2,3 , three axis
5).Enter Spindle Parameter
Set the motor model code from the parameter  list >parameter No 6633
Automatic parameter initialization function Parameter 6519 bit #7 =1
Step 4&5 will initialize the servo/spindle parameter.
Later restart and verify 65xx & 8nxx with list
6).Enter Diagnostics Parameters
Hope this helps
Last edit: 3 years 9 months ago by sivaraj. Reason: typo and format
3 years 9 months ago #262706 by sivaraj
A860–0309–T302 is a 1024 pulses/rev quadrature encoder used for spindle speed/position feedback .
Attached is Fanuc Connection details
3 years 9 months ago #262779 by new2linux
sivaraj, many thanks. The RS232 port cable is connected in CNC Connector is a (M5). I keyed in the 0 to 900 parameters, I am still working setting the;
"4).Enter Servo parameter you can do this in DGNOS/PARAM button >SV-PRM soft key
or"
I saved by setting PWE = 0, will start fresh tomorrow, starting here:
"in parameter 8n00 & 8n20~8n24
Automatic parameter initialization function Parameter 6519 bit #7 =1"
Will review the parameters to compare to the master list from PC, for correcting.
sivaraj, thank you!
Time to create page: 0.276 seconds